Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

9617 SNMP cards continually falling off the network

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • 9617 SNMP cards continually falling off the network
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:10 PM . Last Modified: ‎2024-03-07 02:11 AM

0 Likes
1
710
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:10 PM . Last Modified: ‎2024-03-07 02:11 AM

9617 SNMP cards continually falling off the network

I have the 9617 SNMP cards that have been failing more and more. I have order more of the new cards but need to get the old ones working at a remote location. I have a tech on-site and we have reseated the card. I see teh mac address in the core switch arp table but it never gets an IP address. I have used teh paperclip reset method to reset to defaults, move the port on the switch, swapped cables and I cannot get it to pick up an IP. I also have teh tech trying locally to configure the card but since its a 9pin serial interface I need a USB adapter. This does not work because teh software that coems with the card assumes com1 which is not the port used when I am using the USB/serial convertor. Any ideas. Would this have to do with teh Comms card which I have had him reset as well.

I also have a card that I can telnet to but I cannot add to the ISX manager. It is setup correctly but wont show up in the manager,.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:10 PM . Last Modified: ‎2024-03-07 02:11 AM

0 Likes
0
711
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:10 PM . Last Modified: ‎2024-03-07 02:11 AM

hi

to begin - the "paper clip method" you mentioned, to reset to defaults, does not reset the card to defaults. it is merely used in the [password reset procedure|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=7879] as well as just forcing a management interface reboot (warmstart) which does not change any values.

by default, these cards come configured with a DHCP cookie enabled. it is Option 43 on a DHCP server. if you do not disable this cookie option, the card will NOT receive an IP address automatically. [click here to view the quick start guide|http://www.apcmedia.com/salestools/ASTE-6Z5QDZ_R0_EN.pdf] to help you with that - page 14 in the PDF. [this guide can help you with checking the Status and link LEDs to see what the card is currently doing|http://www.apcmedia.com/salestools/ASTE-6Z5QEW_R0_EN.pdf]

i suggest you take a look at [this APC knowledgebase article|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=3061] which goes over all initial setup options in detail.

hope this helps!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:10 PM . Last Modified: ‎2024-03-07 02:11 AM

0 Likes
0
712
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:10 PM . Last Modified: ‎2024-03-07 02:11 AM

hi

to begin - the "paper clip method" you mentioned, to reset to defaults, does not reset the card to defaults. it is merely used in the [password reset procedure|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=7879] as well as just forcing a management interface reboot (warmstart) which does not change any values.

by default, these cards come configured with a DHCP cookie enabled. it is Option 43 on a DHCP server. if you do not disable this cookie option, the card will NOT receive an IP address automatically. [click here to view the quick start guide|http://www.apcmedia.com/salestools/ASTE-6Z5QDZ_R0_EN.pdf] to help you with that - page 14 in the PDF. [this guide can help you with checking the Status and link LEDs to see what the card is currently doing|http://www.apcmedia.com/salestools/ASTE-6Z5QEW_R0_EN.pdf]

i suggest you take a look at [this APC knowledgebase article|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=3061] which goes over all initial setup options in detail.

hope this helps!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore