208/120 volt supply vs 240/120 volt supply

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • 208/120 volt supply vs 240/120 volt supply
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 10:54 PM . Last Modified: ‎2024-03-06 03:35 AM

0 Likes
4
1097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:54 PM . Last Modified: ‎2024-03-06 03:35 AM

208/120 volt supply vs 240/120 volt supply

I have an older APC UPS model number SYAF16KRMT currently connected to a 208 volt feeder.  I would like to know if the current connection without modification could be powered in an emergency situation with a 240 volt power feed.  Any assistance is greatly appreciated.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • back-ups
  • feeder
  • generator
  • power
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
mitsmith_apc
Lt. Commander mitsmith_apc
Lt. Commander

Posted: ‎2021-06-30 10:54 PM . Last Modified: ‎2024-03-06 03:34 AM

0 Likes
0
1097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:54 PM . Last Modified: ‎2024-03-06 03:34 AM

Hi Chris,

Yes it will only be when the generator is supplying the power that you will experience issues. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-30 10:54 PM . Last Modified: ‎2024-03-06 03:35 AM

0 Likes
0
1097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:54 PM . Last Modified: ‎2024-03-06 03:35 AM

The rating of the equipment is 120/208, 120/240

Reply

Link copied. Please paste this link to share this article on your social media post.

mitsmith_apc
Lt. Commander mitsmith_apc
Lt. Commander

Posted: ‎2021-06-30 10:54 PM . Last Modified: ‎2024-03-06 03:35 AM

0 Likes
0
1097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:54 PM . Last Modified: ‎2024-03-06 03:35 AM

Hi Chris,

The symmetra Lx can take 208 or 240. When you get the 240volts in the unit will still output whatever you have it set at (I am guessing 208volts). The issue is when you have 240V in and 208V out you will likely get a bypass out of range error message. If the unit has a reason to go to bypass (overload or other internal fault) it will not transfer and will just drop your load. It is designed to do this to protect your load from a sudden jump in voltage (208 to 240). 

As a standard we always recommend outputting the same voltage that you are inputting (208 in 208 out or 240 in 240 out) to prevent any abnormal behavior with the unit.  

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 10:54 PM . Last Modified: ‎2024-03-06 03:34 AM

0 Likes
0
1097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:54 PM . Last Modified: ‎2024-03-06 03:34 AM

Thank you Mike.  That is exactly as we thought.  To be sure, in this case, this will only occur when the automatic standby generator is in use to power the UPS (extremely rarely).  I feel safe that we will not cause harm to the UPS.   

Reply

Link copied. Please paste this link to share this article on your social media post.

mitsmith_apc
Lt. Commander mitsmith_apc
Lt. Commander

Posted: ‎2021-06-30 10:54 PM . Last Modified: ‎2024-03-06 03:34 AM

0 Likes
0
1098
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:54 PM . Last Modified: ‎2024-03-06 03:34 AM

Hi Chris,

Yes it will only be when the generator is supplying the power that you will experience issues. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2024 Schneider Electric, Inc