2 questions: ISX Manager and AP9617 NMC

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • 2 questions: ISX Manager and AP9617 NMC
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:35 PM

0 Likes
8
1256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:35 PM

2 questions: ISX Manager and AP9617 NMC

We've got an ISX Manager server that I'm trying to set up as the trap receiver for all our APC UPS's. So far, I've only been able to get one of them to properly work. Whenever I do a discovery for the IP addresses of the others, I receive one of several errors: Ping failure (despite me being able to do so myself), SNMP failure (despite it being configured on the UPS itself), or SNMP timeout. Any suggestions?

Also, I've deployed a few of the AP9617 NMCs and configured them, but now I am no longer able to access them via Telnet or Web interface. They are on the network as I can ping them, but the interfaces are inaccessible. I've tried resetting the card multiple times but it is basically locked itself from any external access method. What gives or how can I reset to factory defaults?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • _reset
  • ap9617
  • factory
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:34 PM

0 Likes
0
1255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:34 PM

We've got an ISX Manager server that I'm trying to set up as the trap receiver for all our APC UPS's. So far, I've only been able to get one of them to properly work. Whenever I do a discovery for the IP addresses of the others, I receive one of several errors: Ping failure (despite me being able to do so myself), SNMP failure (despite it being configured on the UPS itself), or SNMP timeout. Any suggestions?

Also, I've deployed a few of the AP9617 NMCs and configured them, but now I am no longer able to access them via Telnet or Web interface. They are on the network as I can ping them, but the interfaces are inaccessible. I've tried resetting the card multiple times but it is basically locked itself from any external access method. What gives or how can I reset to factory defaults?

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 8
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:35 PM

0 Likes
0
1255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:35 PM

Hello,

Regarding the cards with the ISX Manager, are they on the public side of your network, or on the APC private side? Are the Usernames and Passwords the same as the one that IS working and found by ISX Manager? Are they all the same version of Firmware on the card?

With the AP9617's, can you start an FTP session with them? If so, and can get in using the Username and Password, you can try to do a firmware upgrade on those, hoping that it is just an AOS error that is not allowing for the interface to load. However, you may have to do a physical reset on it by following the K-base.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:35 PM

0 Likes
0
1255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:35 PM

I tried a physical reset of one of the units and that finally got the interfaces to come up. I thought I had done that once before, but apparently not. After doing so, I was finally then able to get the ISX Manager to recognize it.

As for the firmware/AOS, they are all the same (3.5.5) except for the 2 Symmetra PX systems we have, I believe they are 3.3.1 except they are the ones now that I'm not able to access. I'm thinking they will have to be put in some kind of maintenance bypass mode to get the cards to reset similar to the process with the Smart-UPS I just did.

EDIT: By the way, all the units are on the public domain except for the Symmetra system that is physically connected to the ISX Manager (that's another issue I'm working on). And they are all also still running on the default username/password.

Message was edited by: gdavidson79

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:35 PM

0 Likes
0
1255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:35 PM

Hello,

Good to hear, are you still experiencing any problems with the integration of these with ISX Manager?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:35 PM

0 Likes
0
1255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:35 PM

KMP,

Yes, I was finally able to get the Symmetra (v3.3.1) loaded into ISX Manager with some help from APC support. Turns out it doesn't like misspelled community names...ha ha. I swear I looked at those settings until my eyes bled but it is now up and running. Thanks again for your advice.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:34 PM

0 Likes
0
1255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:34 PM

Greg,

Excellent. Next time if there's a problem, if you haven't already ventured into it, I would start an FTP session with the card that is working, and do a "get config.ini" and take a look at that configuration in the community names section, then match that to a config (by doing the same thing), of another one that isn't working. You can re-up an edited config file after you make changes to it, so that essentially, you can just take the config that works, change the IP address, and re-load it to another card.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:34 PM

0 Likes
0
1255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:34 PM

I had an NMC that wasn't on the ISX. I upgraded the firmware to 3.5.8. It lives on a 1000RM2U.

Before the upgrade, I was able to http to the NMC. Even after the upgrade, I could access the GUI. But then I added it to the ISX and now I can't talk to it anymore.

What gives? Doesn't the reset button actually factory default the NMC??? I must be doing something wrong because even after hitting the reset button, it responds (ping) on the same IP. I can't log in using apc/apc or any other username and password that I've used.

How do I actually do a factory reset on that NMC?

Any help from the pros would be appreciated. Thanks in advance.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:34 PM

0 Likes
0
1255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:34 PM

Hi Sonnyali,
Sounds like something might have happened during the firmware upgrade. Since it responds to ping, it should still have the same ip. I would try to reflash the firmware first, if that doesn't work, it might be best to connect to it through the ups' serial interface. This way we can check a few things and determine if the firmware upgrade has taken out the ftp/web server interfaces.

You will need the black 940-0024 serial cable that came with the unit and a computer with a serial port or usb to serial converter. The port settings you will need to use are as follows 2400,8,n,1. Once connected, hit the enter key a few times to pull up a login prompt. Once you've logged in, verify that the status of the card is P+N+A+. If it is anything else, you will need to reflash the firmware, possibly through the serial interface. You can find the instructions here:

http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=768

All the reset button on the card does is reboot the network interface and temporarily reset the username. To reset it to defaults, you can only do that through the web, telnet, or serial interfaces. Hope this helps, let us know if you need any further assistance.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:34 PM

0 Likes
0
1256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:03 AM . Last Modified: ‎2024-03-07 11:34 PM

We've got an ISX Manager server that I'm trying to set up as the trap receiver for all our APC UPS's. So far, I've only been able to get one of them to properly work. Whenever I do a discovery for the IP addresses of the others, I receive one of several errors: Ping failure (despite me being able to do so myself), SNMP failure (despite it being configured on the UPS itself), or SNMP timeout. Any suggestions?

Also, I've deployed a few of the AP9617 NMCs and configured them, but now I am no longer able to access them via Telnet or Web interface. They are on the network as I can ping them, but the interfaces are inaccessible. I've tried resetting the card multiple times but it is basically locked itself from any external access method. What gives or how can I reset to factory defaults?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of