1400RM2U Constant Beep

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • 1400RM2U Constant Beep
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 02:47 AM . Last Modified: β€Ž2024-02-14 10:45 PM

0 Likes
4
1891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:47 AM . Last Modified: β€Ž2024-02-14 10:45 PM

1400RM2U Constant Beep

I heard a solid beep coming from one of my racks last week, and discovered that it was a Smart-UPS 1400RM2U. Turning the power off alone didn't stop the beep - I had to also unplug the battery tray.

I replaced the batteries, but as soon as I plugged in the tray, the beeping started again.. even before powering on the unit. I used the WebUI to access the logs, and there's nothing out of the ordinary. The interface says everything is fine... the loud solid beep says otherwise.

If I plug in the main outlet without the battery tray hooked up, the unit is unresponsive. As soon as I connect the batteries, regardless of whether or not it's plugged into the wall, it beeps.

I've opened the unit and all the caps visually look OK.

Any ideas on where to start troubleshooting?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • beep
  • smart-ups
  • solid
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 02:48 AM . Last Modified: β€Ž2024-02-14 10:45 PM

0 Likes
0
1890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:48 AM . Last Modified: β€Ž2024-02-14 10:45 PM

Steve,

Let me know how it goes.

Tom

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 02:48 AM . Last Modified: β€Ž2024-02-14 10:45 PM

0 Likes
0
1890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:48 AM . Last Modified: β€Ž2024-02-14 10:45 PM

Hey Steve,

Sorry to hear your having some trouble.

The constant tone coming from the unit usually indicates a overload on the unit, meaning the attached equipment is drawing more power than the unit is designed to support. However if there was an overload you should see this reflected in the web interface and in the logs. Additionally, these older style units require good batteries installed in the unit to be able to turn on, simply plugging the unit into the wall without the batteries attached will give no response.

First I would try is to remove the attached devices one by one to see if constant tone stops. If that doesn't yield any good results we can try to reset the unit via a Brain Dead.

To do this;

  1. disconnect all attached devices,
  2. unplug the unit from the wall,
  3. press and hold the OFF button,
  4. you may hear a click and see the LEDs flash,
  5. then plug the unit back into the wall and power on the unit.

Let me know how you make out.

Cheers, Tom

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 02:48 AM . Last Modified: β€Ž2024-02-14 10:45 PM

0 Likes
0
1889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:48 AM . Last Modified: β€Ž2024-02-14 10:45 PM

Thanks, Tom. The problem occurred even with no loads.

But it's been sitting here powered off in my office for a few days, and when I fired it up just now to test this... seems to be working fine. LOL

I'll run some tests on it now...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 02:48 AM . Last Modified: β€Ž2024-02-14 10:45 PM

0 Likes
0
1889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:48 AM . Last Modified: β€Ž2024-02-14 10:45 PM

Well, OK. Seems it needed to sit dead in my office for a while! πŸ™‚

Doing a runtime calibration on it now... I'll be watching closely. πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 02:48 AM . Last Modified: β€Ž2024-02-14 10:45 PM

0 Likes
0
1891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:48 AM . Last Modified: β€Ž2024-02-14 10:45 PM

Steve,

Let me know how it goes.

Tom

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore