Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
10kV APC UPS WAS SHUTDOWN AFTER 2MINUTE
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-0901:20 AM
Hello,
The batteries needs to be exposed to 2 or 3 charge/discharge cycles to update the battery constant
We recommends to follow the below procedures:
- brain dead the unit after disconnecting the loads to reset the control logic
-Then start up the UPS again and insert the loads (should be min 30 %)
-Ensure you changed the battery replacement date from UPS NMC
-Then perform start up test, once passed
-Leave the batteries to charge for 48 hours
-Then perform runtime calibration test with same 30 % load from the NMC
-Once passed leave the batteries to charge for 24 hours
-Then perform discharge test by disconnecting the UPS input mains with the same 30% load
-Leave the batteries to discharge until the connected loads shutdown even if the battery LED lit up this will allow the controller to update battery runtime constant
-then return back mains to the UPS and let the UPS charge the batteries for 24 hours while maintain the desired load level 30 %
we usually instruct this to our service centers to perform the procedures using load bank or dummy load
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-0901:20 AM
Hello,
The batteries needs to be exposed to 2 or 3 charge/discharge cycles to update the battery constant
We recommends to follow the below procedures:
- brain dead the unit after disconnecting the loads to reset the control logic
-Then start up the UPS again and insert the loads (should be min 30 %)
-Ensure you changed the battery replacement date from UPS NMC
-Then perform start up test, once passed
-Leave the batteries to charge for 48 hours
-Then perform runtime calibration test with same 30 % load from the NMC
-Once passed leave the batteries to charge for 24 hours
-Then perform discharge test by disconnecting the UPS input mains with the same 30% load
-Leave the batteries to discharge until the connected loads shutdown even if the battery LED lit up this will allow the controller to update battery runtime constant
-then return back mains to the UPS and let the UPS charge the batteries for 24 hours while maintain the desired load level 30 %
we usually instruct this to our service centers to perform the procedures using load bank or dummy load
Regards,
Karim