10kV APC UPS WAS SHUTDOWN AFTER 2MINUTE

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • 10kV APC UPS WAS SHUTDOWN AFTER 2MINUTE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
ZEKEY
ZEKEY
Cadet

Posted: ‎2024-12-31 11:36 AM

0 Likes
1
402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-31 11:36 AM

10kV APC UPS WAS SHUTDOWN AFTER 2MINUTE

10kV APC UPS WAS SHUTDOWN AFTER 2MINUTE EVEN IF BATTERY WAS CHANGED BY THE NEW COULD YOU HELP ME PLEASE

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-03-09 01:20 AM

1 Like
0
332
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-09 01:20 AM

Hello,

 

The batteries needs to be exposed to 2 or 3 charge/discharge cycles to update the battery constant 

 

We recommends to follow the below procedures:

 

- brain dead the unit after disconnecting the loads to reset the control logic

-Then start up the UPS again and insert the loads (should be min 30 %)

-Ensure you changed the battery replacement date from UPS NMC 

-Then perform start up test, once passed

-Leave the batteries to charge for 48 hours

-Then perform runtime calibration test with same 30 % load from the NMC 

-Once passed leave the batteries to charge for 24 hours

-Then perform discharge test by disconnecting the UPS input mains with the same 30% load

-Leave the batteries to discharge until the connected loads shutdown  even if the battery LED lit up this will allow the controller to update battery runtime constant

-then return back mains to the UPS and let the UPS charge the batteries for 24 hours while maintain the desired load level 30 %

 

we usually instruct this to our service centers to perform the procedures  using load bank or dummy load 

 

Regards,

Karim

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-03-09 01:20 AM

1 Like
0
333
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-09 01:20 AM

Hello,

 

The batteries needs to be exposed to 2 or 3 charge/discharge cycles to update the battery constant 

 

We recommends to follow the below procedures:

 

- brain dead the unit after disconnecting the loads to reset the control logic

-Then start up the UPS again and insert the loads (should be min 30 %)

-Ensure you changed the battery replacement date from UPS NMC 

-Then perform start up test, once passed

-Leave the batteries to charge for 48 hours

-Then perform runtime calibration test with same 30 % load from the NMC 

-Once passed leave the batteries to charge for 24 hours

-Then perform discharge test by disconnecting the UPS input mains with the same 30% load

-Leave the batteries to discharge until the connected loads shutdown  even if the battery LED lit up this will allow the controller to update battery runtime constant

-then return back mains to the UPS and let the UPS charge the batteries for 24 hours while maintain the desired load level 30 %

 

we usually instruct this to our service centers to perform the procedures  using load bank or dummy load 

 

Regards,

Karim

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore