APC PDU AP7953 - internal flash/EEPROM corruption - loss of model data and MAC ADDRESS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC PDU AP7953 - internal flash/EEPROM corruption - loss of model data and MAC ADDRESS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Thehopefulchurchtech
Crewman Thehopefulchurchtech
Crewman

Posted: ‎2025-02-27 02:15 AM

0 Likes
7
1196
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-27 02:15 AM

APC PDU AP7953 - internal flash/EEPROM corruption - loss of model data and MAC ADDRESS

Hello, if this is not the right forum section , admins please move.

 

I have just acquired 3 AP7953 PDU for a church project. having been told there are functional they are not. The internal "factory" setting for Model, Serial number, MAC address when interrogated via the serial port are corrupt. 

 

I can manually set IP address and ping the units, but that is all the ethernet functionality I can get. 

 

I can turn on 8 of the 24 ports via the serial, these are the only ones the unit recognises. I suspect because they didnt know what model they are.

 

Please Please Please -  is there a way of restoring the factory models, serial and MAC address to what otherwise are  working units. If there is not these are going to end up as WEE waste. 

 

Please can APC/Schneider do the moral thing and provide a process to resurrect these units in a day and age when the environment is key.

The units must have been individually loaded in the factory with these setting post build as the boards appear to be universal across models.

I am happy to sign NDAs stating that information is not to be shared or used for commercial benefit.

thanks in advance for any assistance.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
Teken
Kirk Teken
Kirk

Posted: ‎2025-02-27 08:45 AM

0 Likes
5
1192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-27 08:45 AM

This hardware has been EOL since 2022. As such does not have formal APC technical support.

 

Its obvious the PDU’s were sold because they are faulty. Your choices are to obtain the last firmware release for this specific PDU and see if it helps restore the equipment or replace the NMC inside.

 

From personal experience the NMC is physically bad and reflashing the firmware doesn’t resolve the issue.

 

In the interim if one of the PDU NMC is working swap it over to the other. If the swap resolves the problem you found the issue (Bad NMC).

 

If however swapping in a working NMC does NOT resolve the issue there are other hardware issues present! ☝️

 

You may consider submitting a service request to obtain the last firmware release and giving it a try.

 

Questions Ask . . . 👍 

Reply

Link copied. Please paste this link to share this article on your social media post.

Thehopefulchurchtech
Crewman Thehopefulchurchtech
Crewman

Posted: ‎2025-02-27 11:35 AM

In response to Teken
0 Likes
4
1156
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-27 11:35 AM

As described above the "hardware" all looks good. The issue i belive can not be solved with a basic firmware refresh. Even if I do this the unit still wont know its MAC address or  model number. 

What I am hoping for is the maintenance / service / factory back door for loading this data. As you say these are EOL so there is no real reason for APC to not release a process. Especaliy if it can only be done via the serial port. i.e. right with the unit. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-02-28 07:03 AM

In response to Thehopefulchurchtech
0 Likes
3
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-28 07:03 AM

All three NMC on the PDU have the same problem?!?

Reply

Link copied. Please paste this link to share this article on your social media post.

Thehopefulchurchtech
Crewman Thehopefulchurchtech
Crewman

Posted: ‎2025-03-01 01:33 AM

In response to Teken
0 Likes
2
1103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-01 01:33 AM

Yes all three appear to have corrupt epprom data around model and mac address to varrying degrees two the model amd mac all zeros. The other has a radndom mac address and random characters for the model number.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-03-02 11:15 PM

In response to Thehopefulchurchtech
0 Likes
1
1100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-02 11:15 PM

Do all three allow you to access the internal webpage of the NMC? If so show me the About tab for the hardware. 

What happens when you default the unit to a factory state?!?

Reply

Link copied. Please paste this link to share this article on your social media post.

Thehopefulchurchtech
Crewman Thehopefulchurchtech
Crewman

Posted: ‎2025-03-03 12:25 AM

In response to Teken
0 Likes
0
1088
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-03 12:25 AM

No.. i cant get to the internal web page. The best I can do is Ping them once I set up manual IP settings. They wont DHCP. 

Fractoy reset defults back to no IP settings.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Thehopefulchurchtech
Crewman Thehopefulchurchtech
Crewman

Posted: ‎2025-03-09 06:57 AM

0 Likes
0
1046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-09 06:57 AM

Okay -  I found a fix  to some of the bricked AP7953 which corrupted EPPROMS. The 4 units I have had 2 different versions of the processor board. But they both have a 128Kb I2C EPROM. This contains the unit identity and user settings etc. Without this being right the unit wont boot to be the correct model. On the type where the EPPROM is under the Battery, you can lift the Batter and read and write the chip in stitu using  suitable programmer (I use the CH341a Mini programmer) on the other type where the chip is off on its own it needs to be lifted from the board. 

 

The following is a read out from a working chip. The section in black shows where the MAC address is stored. I was able to alter to match the serial numbers and mac address of the other units and rewrite their chip and 2 of the dead  unit are now working. I have however got a failed firmware update on one of the others  

Corrupt System info serial readout

Thehopefulchurchtech_1-1741527688831.png

Its Corrupt EPPROM read out

Thehopefulchurchtech_3-1741527984730.png

working readout

Thehopefulchurchtech_2-1741527906621.png

EPPROM Dump for working unit

Thehopefulchurchtech_4-1741528065218.png

Amended to fix another unit

Thehopefulchurchtech_0-1741527397391.png

This was fairly major surgery... but thought I would post as may help others

board type 1 epprom.jpg

 

board type 2 epprom.jpg

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.