Hello Good people,
I have a 40KVA smart-UPS VT which was installed to a 400 volt, 3 phase and neutral supply very recently. It indicated a site wiring fault. the phase rotation was corrected not before the batteries got discharged.
Phase rotation has now been corrected and batteries in the modules replaced but,
The fault led still shows red and the site wirng fault and output power turned off and batteries discharged still display and ups would not start.
How do we clear this messages in memory/Reset?.
How do we restart this UPS?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:51 PM . Last Modified: 2024-03-07 01:57 AM
Yes I would turn off power to the UPS to reset the logic and see what happens. I'm assuming you don't have any load connected yet as you couldn't have gotten the UPS online with incorrect phase rotation.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:51 PM . Last Modified: 2024-03-07 01:57 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:51 PM . Last Modified: 2024-03-07 01:57 AM
Hello Good people,
I have a 40KVA smart-UPS VT which was installed to a 400 volt, 3 phase and neutral supply very recently. It indicated a site wiring fault. the phase rotation was corrected not before the batteries got discharged.
Phase rotation has now been corrected and batteries in the modules replaced but,
The fault led still shows red and the site wirng fault and output power turned off and batteries discharged still display and ups would not start.
How do we clear this messages in memory/Reset?.
How do we restart this UPS?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:51 PM . Last Modified: 2024-03-07 01:57 AM
Yes I would turn off power to the UPS to reset the logic and see what happens. I'm assuming you don't have any load connected yet as you couldn't have gotten the UPS online with incorrect phase rotation.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of