Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-30 07:51 PM . Last Modified: 2024-03-07 01:57 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:51 PM . Last Modified: 2024-03-07 01:57 AM
Hello Good people,
I have a 40KVA smart-UPS VT which was installed to a 400 volt, 3 phase and neutral supply very recently. It indicated a site wiring fault. the phase rotation was corrected not before the batteries got discharged.
Phase rotation has now been corrected and batteries in the modules replaced but,
The fault led still shows red and the site wirng fault and output power turned off and batteries discharged still display and ups would not start.
How do we clear this messages in memory/Reset?.
How do we restart this UPS?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:51 PM . Last Modified: 2024-03-07 01:57 AM
Yes I would turn off power to the UPS to reset the logic and see what happens. I'm assuming you don't have any load connected yet as you couldn't have gotten the UPS online with incorrect phase rotation.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:51 PM . Last Modified: 2024-03-07 01:57 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:51 PM . Last Modified: 2024-03-07 01:57 AM
Hello Good people,
I have a 40KVA smart-UPS VT which was installed to a 400 volt, 3 phase and neutral supply very recently. It indicated a site wiring fault. the phase rotation was corrected not before the batteries got discharged.
Phase rotation has now been corrected and batteries in the modules replaced but,
The fault led still shows red and the site wirng fault and output power turned off and batteries discharged still display and ups would not start.
How do we clear this messages in memory/Reset?.
How do we restart this UPS?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:51 PM . Last Modified: 2024-03-07 01:57 AM
Yes I would turn off power to the UPS to reset the logic and see what happens. I'm assuming you don't have any load connected yet as you couldn't have gotten the UPS online with incorrect phase rotation.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.