APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-06-28 04:37 AM . Last Modified: 2024-03-18 04:17 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:37 AM . Last Modified: 2024-03-18 04:17 AM
I am getting a compensating for high voltage on only 1 unit in my facility. but the voltage is not exceeding the threshold of 127.
thoughts?
0x010D
Serial Number :
Device Serial Number :
Date : 04/23/2016
Time : 22:29:37
Code : 0x010D
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:37 AM . Last Modified: 2024-03-18 04:16 AM
Alan,
127 is a low setting and I see that there are a few entries in the data log at 125.19 so it is possible the voltage bumped up higher. Set the threshold to 130 and monitor it. That should resolve the issue.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:37 AM . Last Modified: 2024-03-18 04:17 AM
Alan,
What is the exact model Smart-UPS? You will find the information on the bar code stick on the back of the unit.
Also, is there a network management card in the UPS? If there is it would be helpful to review the data and event logs.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:37 AM . Last Modified: 2024-03-18 04:17 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:37 AM . Last Modified: 2024-03-18 04:17 AM
serial number ZA1544070185
device serial 3S1550X01309
its a UPS 1000/1500VA
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:37 AM . Last Modified: 2024-03-18 04:17 AM
Alan,
Is there a network card in the Smart-UPS. It would be helpful to see the event and data logs. Also, what is the exact model number? Examples: SMT1000, SMX1000
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:37 AM . Last Modified: 2024-03-18 04:16 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:37 AM . Last Modified: 2024-03-18 04:16 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:37 AM . Last Modified: 2024-03-18 04:16 AM
Notice the threshold isn't passing the 127 and it triggers high voltage.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:37 AM . Last Modified: 2024-03-18 04:16 AM
Alan,
127 is a low setting and I see that there are a few entries in the data log at 125.19 so it is possible the voltage bumped up higher. Set the threshold to 130 and monitor it. That should resolve the issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.