"Bacnet point" From EBO auto write to KNX bus when "spacelynk" connected !
SpaceLogic KNX Forum
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • "Bacnet point" From EBO auto write to KNX bus when "spacelynk" connected !
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
60
Heribert_Dölger
31
SpaceLogic KNX - 4ʺ Touch Unit
KNX Push Button Dynamic Labeling, universal
Wiser for KNX : logic controller
Back to SpaceLogic KNX Forum
thien_daotho_mi
Crewman thien_daotho_mi
Crewman
Posted: ‎2021-06-08 02:17 AM . Last Modified: ‎2024-07-14 11:47 PM
738
Hi guy,
I have a problem when intergrated Spacelynk and EBO.  When Spacelynk connected, Bacnet Point From EBO auto write to KNX bus ( Random not Last value). Can you help me how to disable this property or configure write last value.
  • Thumbnail of SpaceLogic KNX - 4ʺ Touch Unit
  • Thumbnail of KNX Push Button Dynamic Labeling, universal
  • Thumbnail of Wiser for KNX : logic controller
View products (3)
  • Protocols
Erwin-vd-Zwart
Janeway
Posted: ‎2021-06-10 11:56 PM
732
What did you set as default priority in the spaceLYnk? System -> Network -> BACnet settings -> Object priority
Make sure to make your bindings in EBO to this priority. (default this is 16).
Another thing to check is the advanced polling configuration on your BACnet interface, set the min polling interval to 1000 ms
BR,
Erwin
Erwin-vd-Zwart
Janeway
733
BR,
Erwin
thien_daotho_mi
Crewman
Posted: ‎2021-06-11 08:10 AM
Thanks for your support. I set "Bacnet Priority" in Spacelynk is 16 and when bind to EBO some Bacnet Point's Priority change to 10. Maybe during Install system, i made a mistake something. I deleted, reinstalled and it's ok.
Thank you so much,