motion detector Alarm

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • motion detector Alarm
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Related Products
product field
SpaceLogic KNX - 4ʺ Touch Unit
product field
KNX Push Button Dynamic Labeling, universal
product field
Wiser for KNX : logic controller

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Start a Topic
Solved
IC_Systems
Captain IC_Systems
Captain

Posted: ‎2021-10-25 06:10 AM . Last Modified: ‎2024-07-14 11:45 PM

0 Likes
3
719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-25 06:10 AM

motion detector Alarm

Hello Community

 

I have a project where the motion will have two jobs:

- Alarm when intrusion system activated (intrusion system)

- control the lights and AC when 

 

I think using the MTN630719 or another SE KNX Motion detector but I know from the manual it's not recommended.

Also, I think installing a separate intrusion system like  paradox and integrating it with KNX, but I don't know if it will fulfill the requirements

 

what do you suggest?

 

BR,

 

Best Regards,
  • Thumbnail of SpaceLogic KNX - 4ʺ Touch Unit
    SpaceLogic KNX - 4ʺ Touch Unit
  • Thumbnail of KNX Push Button Dynamic Labeling, universal
    KNX Push Button Dynamic Labeling, universal
  • Thumbnail of Wiser for KNX : logic controller
    Wiser for KNX : logic controller
View products (3)
Labels
  • Labels:
  • SpaceLYnk
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2021-10-25 06:45 AM

1 Like
2
717
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-25 06:45 AM

Hello nasser_ic-systems,

 

the reason why it is not recommended is that you can face false alarms due to a quick temperature change (for whatever reason) or even effects with lights. We are using here the passive infrared technology which is working with tmeperature changes.
Means such kind of possible false alarms can trigger the police or security service which causes some useless costs and trouble.

Therefor it is good to use the recommended motion sensors of the security system which may use another detection technology.

So I would recommend to seperate the systems (alarm and building management).

I would not recommend to use only the motion sensor of the security system for building management puposes.
Because in case you get the information from the security system that a motion sensor is tripped you may not know the local conditions like e.g. brightness, when the motion really occured the last time to start a staircase time and many other feature of our motion devices. As well controlling lights by one channel and HVAC with a second channel needs to be realised seperately somehow. Not that easy ... be carefull with that.

 

Kind regards
Thomas

Application Design Engineer

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 3
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2021-10-25 06:45 AM

1 Like
2
718
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-25 06:45 AM

Hello nasser_ic-systems,

 

the reason why it is not recommended is that you can face false alarms due to a quick temperature change (for whatever reason) or even effects with lights. We are using here the passive infrared technology which is working with tmeperature changes.
Means such kind of possible false alarms can trigger the police or security service which causes some useless costs and trouble.

Therefor it is good to use the recommended motion sensors of the security system which may use another detection technology.

So I would recommend to seperate the systems (alarm and building management).

I would not recommend to use only the motion sensor of the security system for building management puposes.
Because in case you get the information from the security system that a motion sensor is tripped you may not know the local conditions like e.g. brightness, when the motion really occured the last time to start a staircase time and many other feature of our motion devices. As well controlling lights by one channel and HVAC with a second channel needs to be realised seperately somehow. Not that easy ... be carefull with that.

 

Kind regards
Thomas

Application Design Engineer
Tags (1)
  • Tags:
  • english
Reply
IC_Systems
Captain IC_Systems
Captain

Posted: ‎2021-10-25 08:08 AM . Last Modified: ‎2021-10-25 08:10 AM

0 Likes
1
715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-25 08:08 AM

Hello @Thomas_Rohde  and thanks for your valuable information.

So I will use a separate intrusion system and integrate it with KNX, while the customer wants to use the Alarm motion to turn off the AC when the office is not occupied (to save some money instead of installing a new KNX Motion).

 

and we already integrated the AC by the intesis DK RC which has the occupancy function on it, and I will just link the Alarm motion signal with the Occupancy function in the intesis (This is what I am thinking about)

so do you have any recommendations or advice regarding this point

 

BR,

Best Regards,
Tags (1)
  • Tags:
  • english
Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2021-10-28 10:59 PM

1 Like
0
707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-28 10:59 PM

Hello nasser_ic-systems,

 

as long as the alarmsystem share always the information "motion detected" independent of the status (armed/disarmed) it should work like that,

 

Kind regards
Thomas

Application Design Engineer
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore