Wiser for KNX - 404 Page not Found

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • Wiser for KNX - 404 Page not Found
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Related Products
product field
SpaceLogic KNX - 4ʺ Touch Unit
product field
KNX Push Button Dynamic Labeling, universal
product field
Wiser for KNX : logic controller

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Start a Topic
Solved
cristianstritzke
Ensign cristianstritzke
Ensign

Posted: ‎2022-04-13 04:05 AM . Last Modified: ‎2024-07-14 11:44 PM

0 Likes
5
2096
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-04-13 04:05 AM

Wiser for KNX - 404 Page not Found

Hi, i'm Cristian from Argentina.

I have a problem with my Wiser for knx. It was working good for 1 year, and now I need to change te ip of the Wiser. When i go to seetings, in the configuración of the Wiser, appear a page that Say: 404 not found (all in withe). For this reason i have reset the wiser to defaults, and now, when I Enter in the IP of the Wiser and try to login, it's brings me to the same page 404 not found, so i cant do nothing in the wiser.

 

Any solution?

 

Thanks!

  • Thumbnail of SpaceLogic KNX - 4ʺ Touch Unit
    SpaceLogic KNX - 4ʺ Touch Unit
  • Thumbnail of KNX Push Button Dynamic Labeling, universal
    KNX Push Button Dynamic Labeling, universal
  • Thumbnail of Wiser for KNX : logic controller
    Wiser for KNX : logic controller
View products (3)
Labels
  • Labels:
  • Wiser for KNX
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
cristianstritzke
Ensign cristianstritzke
Ensign

Posted: ‎2022-04-19 04:13 AM . Last Modified: ‎2022-04-19 04:14 AM

1 Like
0
2063
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-04-19 04:13 AM

Hi @Thomas_Rohde. Thanks!

 

The problema was solved. I got in touch with tsc-southamerica@schneider-electric.com

 

They told me, that I have to flash the microSD of the Wiser for KNX.

 

Here is the solution:

 

https://www.se.com/ww/en/download/document/AN2_001_SL/

Very Thanks Thomas.

 

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 5
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2022-04-13 04:18 AM

0 Likes
4
2094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-04-13 04:18 AM

Hi Cristian,

 

can you please provide more details like:
HW-Version of your device > Sticker on the right side of the product

FW-Version you have installed
Picture where we can see the complete URL
Project backup?!

 

Actions

Please clear the cache of your used browser and reach out to the device again.
Can you ping the device to make sure that your device is really still there.
Double check that you are really within the same network as the device.
Because as you want to change the IP it seems you have some changes within your IP-Network.

  

Kind regards
Thomas

Application Design Engineer
Tags (1)
  • Tags:
  • english
Reply
cristianstritzke
Ensign cristianstritzke
Ensign

Posted: ‎2022-04-13 06:24 AM

0 Likes
3
2089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-04-13 06:24 AM

Hi, Thomas, thanks for answering. 

 

I Claer my Cache, and still not working.

 

I attach some pictures of my wiser and the last project Backup.

 

The firmware its the one thats comes by default (I cant see it, because i cant login in wiser).

 

 

Attachments
Tags (1)
  • Tags:
  • english
Reply
cristianstritzke
Ensign cristianstritzke
Ensign

Posted: ‎2022-04-18 03:28 AM

0 Likes
2
2075
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-04-18 03:28 AM

@Thomas_Rohde hi! Any idea?

Tags (1)
  • Tags:
  • english
Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2022-04-19 03:01 AM

0 Likes
1
2065
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-04-19 03:01 AM

Hi Cristian,

 

sorry we had a long easter weekend.

From the picture you sent it seems everything OK.

Strange that the device is not reacting as expected.

 

I couldnt install locally your project-backup as it was not attached.

 

Do you have by ramdom a second device where you could install this backup just for test purposes?
I mean in order to identify if it is, for whatever reason, a HW issue?

 

Kind regards
Thomas

Application Design Engineer
Tags (1)
  • Tags:
  • english
Reply
cristianstritzke
Ensign cristianstritzke
Ensign

Posted: ‎2022-04-19 04:13 AM . Last Modified: ‎2022-04-19 04:14 AM

1 Like
0
2064
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-04-19 04:13 AM

Hi @Thomas_Rohde. Thanks!

 

The problema was solved. I got in touch with tsc-southamerica@schneider-electric.com

 

They told me, that I have to flash the microSD of the Wiser for KNX.

 

Here is the solution:

 

https://www.se.com/ww/en/download/document/AN2_001_SL/

Very Thanks Thomas.

 

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore