KNX TP1-256 Topology

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • KNX TP1-256 Topology
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
121
Erwin-vd-Zwart
Sisko Erwin-vd-Zwart Sisko
54
Heribert_Dölger
Lt. Commander Heribert_Dölger Lt. Commander
30
FZetina
Lt. Commander FZetina Lt. Commander
27
View All
Related Products
product field
SpaceLogic KNX - 4ʺ Touch Unit
product field
KNX Push Button Dynamic Labeling, universal
product field
Wiser for KNX : logic controller

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Solved
IC_Systems
Captain IC_Systems
Captain

Posted: ‎2022-03-30 12:39 AM . Last Modified: ‎2024-07-14 11:44 PM

0 Likes
7
871
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-30 12:39 AM

KNX TP1-256 Topology

Hello,

Could we use the new KNX TP1-256 Topology?

Could you make some explanation, and what is  your recommendation?

 

 

Best Regards,
  • Thumbnail of SpaceLogic KNX - 4ʺ Touch Unit
    SpaceLogic KNX - 4ʺ Touch Unit
  • Thumbnail of KNX Push Button Dynamic Labeling, universal
    KNX Push Button Dynamic Labeling, universal
  • Thumbnail of Wiser for KNX : logic controller
    Wiser for KNX : logic controller
View products (3)
Labels
  • Labels:
  • SpaceLYnk
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Erwin-vd-Zwart
Sisko Erwin-vd-Zwart Sisko
Sisko

Posted: ‎2022-03-30 01:08 AM

2 Likes
6
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-30 01:08 AM

That depands on the products you are using, see the attachment for more details..

 

There has always been two conditions, a max number of devices due to transmission characteristics and the total current consumption of the devices.

 

Let’s start with transmission characteristics:

Since all times we learned that the maximum allowed number of KNX devices connected to a line segment is 64 for signal transmission reasons.

 

It is not true anymore. More devices are possible and this is now also taught in the certification training, maximum is now 256.

 

What is behind this?

 

For KNX twisted pair devices there exist two different transceiver types, which is the electronic part closest to the bus wires and managing the physical layer. You can see an example to the right.

 

They are called TP-64 and TP-256. TP-64 has existed from the beginning of EIB/KNX and TP-256 came some years ago.

So there are a mix on the market, some devices are TP-64 devices and new once are TP-256 devices.

 

They are compatible and can be used on the same KNX line segment without any problem, so nobody noticed the two types.

However, they have different transmission characteristics which affect the signal differently.

 

With only TP-64 devices, the maximum number of devices on one line segment is 64 and with only TP-256 devices a max of 256 devices is possible. It means, with a mix of transceivers, each TP-64 device should be counted as 4 and each TP-256 as 1 and the sum, the so called fan-in must not exceed 256.

 

For example as you see in the table, 63 TP-64 devices gives fan-in 252, which means there is room for one more TP-64 device or four TP-256 devices, which then will result in 67 devices.

 

Whether a device has TP-64 of TP-256 is not an information given or handled by ETS.

 

We have also not given this information in our data sheets in the past.  However, all new devices since some years has TP-256 transceivers and we now give the info.

 

In our product portfolio we have currently both TP-64 and TP-256 devices.

 

The second condition is that the total current consumption of the KNX devices must not be higher than the nominal output current of the power supply.

 

This must be calculated for each line segment as ever before. The maximum nominal current is as you now know 1280 mA

The typical current consumption of a KNX device today is between 7 and 18 mA,

 

Let’s assume an average of 13 mA which leads to a maximum of 100 devices. So out of these 100 devices, how many can be TP-64 to also fulfil the first condition? The answer is that 52 or less of these 100 devices can be TP-64:  52 TP-64 gives 208 fan-in and 48 TP-256 gives 48, which equals 256.

See Answer In Context

Attachments
Tags (1)
  • Tags:
  • english
Reply
Replies 7
Erwin-vd-Zwart
Sisko Erwin-vd-Zwart Sisko
Sisko

Posted: ‎2022-03-30 01:08 AM

2 Likes
6
867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-30 01:08 AM

That depands on the products you are using, see the attachment for more details..

 

There has always been two conditions, a max number of devices due to transmission characteristics and the total current consumption of the devices.

 

Let’s start with transmission characteristics:

Since all times we learned that the maximum allowed number of KNX devices connected to a line segment is 64 for signal transmission reasons.

 

It is not true anymore. More devices are possible and this is now also taught in the certification training, maximum is now 256.

 

What is behind this?

 

For KNX twisted pair devices there exist two different transceiver types, which is the electronic part closest to the bus wires and managing the physical layer. You can see an example to the right.

 

They are called TP-64 and TP-256. TP-64 has existed from the beginning of EIB/KNX and TP-256 came some years ago.

So there are a mix on the market, some devices are TP-64 devices and new once are TP-256 devices.

 

They are compatible and can be used on the same KNX line segment without any problem, so nobody noticed the two types.

However, they have different transmission characteristics which affect the signal differently.

 

With only TP-64 devices, the maximum number of devices on one line segment is 64 and with only TP-256 devices a max of 256 devices is possible. It means, with a mix of transceivers, each TP-64 device should be counted as 4 and each TP-256 as 1 and the sum, the so called fan-in must not exceed 256.

 

For example as you see in the table, 63 TP-64 devices gives fan-in 252, which means there is room for one more TP-64 device or four TP-256 devices, which then will result in 67 devices.

 

Whether a device has TP-64 of TP-256 is not an information given or handled by ETS.

 

We have also not given this information in our data sheets in the past.  However, all new devices since some years has TP-256 transceivers and we now give the info.

 

In our product portfolio we have currently both TP-64 and TP-256 devices.

 

The second condition is that the total current consumption of the KNX devices must not be higher than the nominal output current of the power supply.

 

This must be calculated for each line segment as ever before. The maximum nominal current is as you now know 1280 mA

The typical current consumption of a KNX device today is between 7 and 18 mA,

 

Let’s assume an average of 13 mA which leads to a maximum of 100 devices. So out of these 100 devices, how many can be TP-64 to also fulfil the first condition? The answer is that 52 or less of these 100 devices can be TP-64:  52 TP-64 gives 208 fan-in and 48 TP-256 gives 48, which equals 256.

Attachments
Tags (1)
  • Tags:
  • english
Reply
IC_Systems
Captain IC_Systems
Captain

Posted: ‎2022-03-30 02:22 AM

0 Likes
3
856
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-30 02:22 AM

Thank You @Erwin-vd-Zwart  for the valuable info.

Could you attach the full document if there is?

Also, Is there a  documents classifying the products to TP1-64 and TP1-256?

 

Best Regards,
Tags (1)
  • Tags:
  • english
Reply
Erwin-vd-Zwart
Sisko Erwin-vd-Zwart Sisko
Sisko

Posted: ‎2022-03-30 02:39 AM

0 Likes
0
853
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-30 02:39 AM

No there is no full document classifying the products (at least i have never seen one), i think you need to look into the product documentation of each product.

 

Tags (1)
  • Tags:
  • english
Reply
Erwin-vd-Zwart
Sisko Erwin-vd-Zwart Sisko
Sisko

Posted: ‎2022-03-30 04:49 AM

1 Like
1
850
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-30 04:49 AM

My colleague (Alexander Efremov) brought to my attention this document (see attachment), it's from 2019 but i think it's save to assume that all devices released after that are TP-256 ...

Attachments
Tags (1)
  • Tags:
  • english
Reply
domotiqa
Lt. Commander domotiqa
Lt. Commander

Posted: ‎2022-03-30 05:34 AM

0 Likes
0
843
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-30 05:34 AM

M. Osterman told me about a listing too.

Maybe he has it

Smarthome & Smartbuilding Expert
Tags (1)
  • Tags:
  • english
Reply
Horacio1
Lieutenant JG Horacio1 Lieutenant JG
Lieutenant JG

Posted: ‎2022-03-31 05:09 PM

0 Likes
1
839
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-31 05:09 PM

Thanks for the great information!!!

 

Does this mean that if I just have TP-256 devices I dont need any line repeater?

Tags (1)
  • Tags:
  • english
Reply
Erwin-vd-Zwart
Sisko Erwin-vd-Zwart Sisko
Sisko

Posted: ‎2022-04-01 12:09 AM

0 Likes
0
835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-04-01 12:09 AM

Correct

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of