Hello!
I have a Wiser for knx HW 1 with SW 3.0.0 and want to expose some KNX adresses (room occupied on/off) to bacnet (Siemens DXR2.E18 roomcontroller).
I tick "export" for the KNX adresses, enable the bacnet server and start YABE to monitor the bacnet objects, but nothing is showing (not even finding the Wiser as a unit on the bacnet network). If I start wireshark with a bacnet filter, and then run "Send whois" from YABE, I see my computer sending the whois and the Wiser is responding "i i´m devide id", so it seems the bacnet server on the wiser is up and running, but no unit or objects is seen in YABE.
If i start the "demo server" or "bacnet room simulator", both installed with YABE, those objects is showing up in YABE.
If I open the "Bacnet object" on the Wiser, I see them there, but not on the bacnet side.
Any suggestions?
Regards
Jonas
- Labels:
-
Wiser for KNX
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Solved: As stated above, ineed the server was up and running, but windows firewall prevented the telegrams from reaching the YABE bacnet browser. The example program was running locally, bypassing the firewall. As soon as the wirewall was disabled both the Wiser and the objects turned up in YABE.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Solved: As stated above, ineed the server was up and running, but windows firewall prevented the telegrams from reaching the YABE bacnet browser. The example program was running locally, bypassing the firewall. As soon as the wirewall was disabled both the Wiser and the objects turned up in YABE.