Universal Dimmer Master 2 channel MTN6710-0102 is possible "switch On/Off by "DIM""? Only On is working for me

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • Universal Dimmer Master 2 channel MTN6710-0102 is possible "switch On/Off by "DIM""? Only On is working for me
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Start a Topic
Solved
Alexander_Remteks
Ensign Alexander_Remteks
Ensign

Posted: ‎2024-07-22 08:06 PM

0 Likes
8
2499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-22 08:06 PM

Universal Dimmer Master 2 channel MTN6710-0102 is possible "switch On/Off by "DIM""? Only On is working for me

Hi, I use dimmer mentioned above. Is possible somehow program switch Off by DIM (or "soft Off")? I mean I need my lamps switching off slowly during 4 seconds, changing brightness. My lamps switching On slowly, during 4 seconds changing brightness from 0 to 100%, but switching Off in a second. 

I did not find any switching off logic/curve correction, just dimming times. I set all to 4 sec in my case, but not working as I need. Is it possible by device?

FW version is 3.12. KNX settings in attach.

Thank you.

Attachments
Labels
  • Labels:
  • SpaceLogic devices
Tags (2)
  • Tags:
  • dimmer
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2024-07-24 12:23 AM

0 Likes
4
2466
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-24 12:23 AM

Hello Alexander_Remteks,
I quickly checked it and on my side it is working. So I have (unfortunately in German) the same parameter then you (Dimm object switches Channel => On and Off). As you can see in the telegram logging ... the relative dimming telegram "dimm down" is given to the bus (marked in yellow) and some time later the dimmer switches off and sends the dedicated status for FB Switch and Value Obj.

Thomas_Rohde_0-1721805322049.png

Can you share with me your ETS-Project?

 

Kind regards
Thomas

Application Design Engineer

See Answer In Context

Reply
Replies 8
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2024-07-24 12:23 AM

0 Likes
4
2467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-24 12:23 AM

Hello Alexander_Remteks,
I quickly checked it and on my side it is working. So I have (unfortunately in German) the same parameter then you (Dimm object switches Channel => On and Off). As you can see in the telegram logging ... the relative dimming telegram "dimm down" is given to the bus (marked in yellow) and some time later the dimmer switches off and sends the dedicated status for FB Switch and Value Obj.

Thomas_Rohde_0-1721805322049.png

Can you share with me your ETS-Project?

 

Kind regards
Thomas

Application Design Engineer
Reply
Cristiano_Carli_Ballola
Lt. Commander Cristiano_Carli_Ballola Lt. Commander
Lt. Commander

Posted: ‎2024-07-24 12:57 AM

0 Likes
1
2462
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-24 12:57 AM

Hello Alexander,

is this the "effect" you are looking for?
It is obtained simply by modifying the execution times of a switch command as you have set in the parameters.
In my example I have extended the time to 6s for better video recording.
Dimming object switches channel Dimming object switches channel forces you to keep your sensor button pressed.

Attachments
Reply
Alexander_Remteks
Ensign Alexander_Remteks
Ensign

Posted: ‎2024-07-24 04:52 AM

0 Likes
0
2433
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-24 04:52 AM

Hi, yes, I want finally my light working as at your video. I will attach KNX file to Thomas. Thank you for help.

Alexander

Reply
Alexander_Remteks
Ensign Alexander_Remteks
Ensign

Posted: ‎2024-07-24 04:58 AM

0 Likes
3
2433
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-24 04:58 AM

Hi Thomas, KNX (ETS 6.2) project part regarding dimmer in attach. Info to dimmer is sent from sensor. I decided that sensor setting is the problem, check solution with KNX button, works anyway not correctly - lights switching On during 4 sec as needed but switching off momentarily.

Alexander

 

 

Attachments
Dimmer.7z
Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2024-07-30 02:52 AM

0 Likes
2
2358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-30 02:52 AM

Hello Alexander_Remteks,

I made intensive tests, updated my device to your FW-Version, used your ETS-Project with your Group-Adresses but on my side it is working as expected.
Attached you will find a little video which shows how the light bulb properly dimms up and down in the configured time of 4 seconds.
Are you sure about the connected load?
Did you tried, as a reference, to use a normal light bulb? To exclude any strange LED-Light behaviour.

 

Kind regards
Thomas

Application Design Engineer
Attachments
Reply
Daniel_Becker
Daniel_Becker
Cadet

Posted: ‎2024-10-16 12:50 PM

0 Likes
1
2154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-16 12:50 PM

Hi there!

I did have the same problem with ignoring the dimming times, but it seems almost to work after upgrading to firmware 3.12.0.

Did anyone tried higher values for the timing or does know what the maximum is?

I'm trying to simulate a sunrise, but getting weird behavior

 

2:48.0: works (but seems to be faster than it should be)

2:48.8: starts with (I think) 100% for a short time, than dimming up from the minimum

3:48.0 (or other higher values): no dimming, 100% immediately

 

According to the application the maximum should be 99:59.9. Maybe some kind of overflow?

Currently I am using global dimm timing for scenes (sorry, also in German):

 

riker84_0-1729107749669.png

But it's the same when sending static values to object 8, or configuring it on the channel (scene or switching doesn't matter).

Also I didn't test the other direction in detail, but dimming down seems to work with higher values.

 

Maybe someone has an idea.

 

Best,

Daniel

 

 

 

 

Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2024-10-29 07:54 AM

1 Like
0
2100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-29 07:54 AM

Hi Daniel_Becker!
We tested what you have reported and so we can confirm that there is a bug within the FW.
It seems that no one used this feature since the products are on the market!!

MANY THANKS for the feedback!

The bug is listed an will be solved with one of the next Firmware-Releases.

 

Kind regards
Thomas

Application Design Engineer
Reply
Alexander_Remteks
Ensign Alexander_Remteks
Ensign

Posted: ‎2025-03-13 12:38 AM

0 Likes
0
1780
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-13 12:38 AM

Hi, when new FW will be released for this device? What is the status now?

 

BR,

 

Alexander

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore