Umotion client touch 10" and 7" no longer connect to the Wiser KNX after updating the wiser firmware to 2.8

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • Umotion client touch 10" and 7" no longer connect to the Wiser KNX after updating the wiser firmware to 2.8
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Start a Topic
Solved
KNXperts
Ensign KNXperts
Ensign

Posted: ‎2025-08-22 02:37 AM

0 Likes
19
3660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-22 02:37 AM

Umotion client touch 10" and 7" no longer connect to the Wiser KNX after updating the wiser firmware to 2.8

Hi,

 

I have the below products in a project:
1 x LSS100100 Wiser KNX (firmware 2.8.0)

2 x Umotion client touch 10

3 x Umotion client touch 7

 

And I have the same issue. When the LSS100100 was on firmware version 2.7, SE support previously sent me a special update for the Umotion client touch 10, and a special apk for the Umotion client touch 7. After updating the LSS100100 to 2.8 (because the app Wiser for KNX was discountinued on the play store and app store), the umotion client touch 7 and 10 are not longer connecting to the server. Does the update for the umotion client touch 10 sent above work in our case? And is there an updated apk for the client touch 7 with the new Wiser app?

Thanks.

Labels
  • Labels:
  • Wiser for KNX
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2025-08-26 12:16 AM

1 Like
2
3621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-26 12:16 AM

Hello 

Which firmware is running on your U.motion 10'' TP? You would need 1.4.4 to be compatible with newer version of LSS100100.

For 7'' TP you will need to use KiBro App, find attached. 

 

Best regards

Heribert

See Answer In Context

Attachments
DivusKioskBrowser_1-4_1434.7z
Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2025-08-28 12:26 AM

1 Like
1
3578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-28 12:26 AM

Hello KNXperts!

To "As for the 10" TP, they are already on 1.4.4. "
Thats great!

To "The issue is that the touch app is not showing, only Scheduler and Trends (Check attached photo)."
This means that it is in general working already. That not the complete content is representet can be an issue with the cache. So I would propose to clear it and try again. To clear the cache is always a good idea when content is not represented in the expected way.

To "Another issue we noticed in the new Wiser KNX app after updating to 2.8 is that custom widgets we created for HVAC control, 1-bit feedback for mechanical systems and for curtain control are not showing in the application."
Custom widgets are not supported in general within the mobile App 😟
Here you will find an overview of supported widgets:
https://www.productinfo.schneider-electric.com/wiser-knx/0000956364-wiser-knx-aug/English/Wiser_KNX_... 
Why no support of custom widgets ...
The problem behind is that it is pretty hard to identify the created structure/function out of this custom widget to interpretate/transform it in a dedicated one within the mobile App. For all the widgets in the list above we now exactly how the widget looks like in the TouchVisu including the dedicated datapoints and so we can have dedicated one within the mobile app. Hope you get the point.
In general the list of supported widgets is growing, but the custom widget is really difficult.

 

Sorry to have no better news!

 

Kind regards
Thomas

Application Design Engineer

See Answer In Context

Reply
Replies 19
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2025-08-26 12:16 AM

1 Like
2
3622
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-26 12:16 AM

Hello 

Which firmware is running on your U.motion 10'' TP? You would need 1.4.4 to be compatible with newer version of LSS100100.

For 7'' TP you will need to use KiBro App, find attached. 

 

Best regards

Heribert

Attachments
DivusKioskBrowser_1-4_1434.7z
Reply
KNXperts
Ensign KNXperts
Ensign

Posted: ‎2025-08-27 12:55 AM

0 Likes
2
3599
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-27 12:55 AM

Hello Heribert,

 

Thank you for your answer. We will test with the KiBro app for the 7" TP.

 

As for the 10" TP, they are already on 1.4.4. The issue is that the touch app is not showing, only Scheduler and Trends (Check attached photo).

 

Another issue we noticed in the new Wiser KNX app after updating to 2.8 is that custom widgets we created for HVAC control, 1-bit feedback for mechanical systems and for curtain control are not showing in the application. Does this has to do with the fact that the Wiser KNX app now divides the widgets into sections in the same room (Lights, energy, etc..). How can we remedy to this problem and show these custom widgets again in the Wiser KNX app for mobile phones?

 

Thank you for your help.

Attachments
Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2025-08-28 12:26 AM

1 Like
1
3579
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-28 12:26 AM

Hello KNXperts!

To "As for the 10" TP, they are already on 1.4.4. "
Thats great!

To "The issue is that the touch app is not showing, only Scheduler and Trends (Check attached photo)."
This means that it is in general working already. That not the complete content is representet can be an issue with the cache. So I would propose to clear it and try again. To clear the cache is always a good idea when content is not represented in the expected way.

To "Another issue we noticed in the new Wiser KNX app after updating to 2.8 is that custom widgets we created for HVAC control, 1-bit feedback for mechanical systems and for curtain control are not showing in the application."
Custom widgets are not supported in general within the mobile App 😟
Here you will find an overview of supported widgets:
https://www.productinfo.schneider-electric.com/wiser-knx/0000956364-wiser-knx-aug/English/Wiser_KNX_... 
Why no support of custom widgets ...
The problem behind is that it is pretty hard to identify the created structure/function out of this custom widget to interpretate/transform it in a dedicated one within the mobile App. For all the widgets in the list above we now exactly how the widget looks like in the TouchVisu including the dedicated datapoints and so we can have dedicated one within the mobile app. Hope you get the point.
In general the list of supported widgets is growing, but the custom widget is really difficult.

 

Sorry to have no better news!

 

Kind regards
Thomas

Application Design Engineer
Reply
KNXperts
Ensign KNXperts
Ensign

Posted: ‎2025-09-01 01:35 PM

0 Likes
1
3511
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-01 01:35 PM

The Kibro app worked perfectly thank you! For the 10" TP, they are on firmware 1.4.4. Should the URL to be used in the 10" TP just be http://wiser_IP_address or http://wiser_IP_address/touch or something else?

Thanks!

Reply
KNXperts
Ensign KNXperts
Ensign

Posted: ‎2025-09-01 01:40 PM

0 Likes
0
3511
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-01 01:40 PM

Hi Thomas! Thank you for your answer. About the widgets, that's too bad since the project was handed over quite some time ago and now we have to redo them all over again using the supported widgets, but that's something feasible. We  tried to clear the cache and reboot the system on the 10" TP, and now the 10" TP asks for the username and password. When we input the admin user and password, we have a message that the login is incorrect, although the same credentials are working when we login to the Wiser KNX using a web browser. Thanks for the help!

Reply
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2025-09-03 10:15 PM

0 Likes
0
3467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-03 10:15 PM

You have to enter the full URL (IP address and rest of string that leads to the visu). In addition you need to activate the checkbox "use free URL" otherwise the panel will try to connect to a U.motion server. 

Reply
KNXperts
Ensign KNXperts
Ensign

Posted: ‎2025-09-05 05:01 AM

0 Likes
0
3382
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-05 05:01 AM

2.jpg

3.jpg

4.jpg

1.jpg

    

Hello Heribert,

Thank you for your answer! Unfortunately the TP 10" issue is still not resolved. We disabled password for accessing apps, cleared the cache, and tried several URLs, but nothing is working. Please check the attached screenshots. The touch app is taking a slot, but is invisible and cannot be clicked. The tested URLs are: http://server_ip-address/apps (then we have the scheduler and trends app showing, but touch is hidden) and http://server_ip-address/apps/data/touch (In that case, only a blank white page can be seen). Touch3 app version is 3.18.7 (20250523). Since the touch3 is not showing, and if we point in the URL to the touch3 app directly, we get a white image, I assume this is a compatibility issue.

I remember we had the same behavior in the past before updating to 1.4.4 and updating the server, where the touch app was visible, but after opening it, we also had a white page only. Can you please advise? Thank you

Reply
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2025-09-09 01:13 AM

0 Likes
0
3349
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-09 01:13 AM

Hello KNXperts

 

Seems the connection in general is working but the content of the Wiser for KNX cannot be shown.

 

I am not an expert on Wiser for KNX so I do not know what the problem could be caused of. Will try to find a colleague who can help you. 

Reply
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2025-09-09 06:37 AM

0 Likes
0
3333
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-09 06:37 AM

Hello KNXperts

The colleague answered that it looks like a cache problem but as you already tried it is not clear. Maybe you can try to clear cache once again.

You also might try with a secure connection using https command (https://server_ip-address/apps/data/touch/) but depends on the settings in the Wiser4KNX.

On the other hand it is possible that there is incompatibility. As the U.motion touch panels have been discontinued several years ago the new versions of Wiser4KNX are no longer tested with the U.motion panels. Then you might need to downgrade the Wiser4KNX.

Best regards

Reply
KNXperts
Ensign KNXperts
Ensign

Posted: ‎2025-09-09 08:36 AM

0 Likes
0
3307
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-09 08:36 AM

Hello Heribert,

 

Thanks for your message and the follow up! Looking forward to your reply as this has become quite urgent and the end-client is putting pressure to finalize this as soon as possible. 

 

Kind regards.

Reply
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2025-09-11 01:16 AM

0 Likes
0
3282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-11 01:16 AM

Hello

 

Did you try above mentioned hints (clear cache again and try with https connection)?

 

Best regards

Reply
KNXperts
Ensign KNXperts
Ensign

Posted: ‎2025-09-15 07:57 AM

0 Likes
0
3215
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-15 07:57 AM

Hello Heribert,

No we have not tried yet the https with the clear cache, but will try to test it as soon as possible. In case there is incompatibility, and we have to downgrade the wiser, will the new app "Wiser KNX" work (Since the old app "Wiser for KNX" is no longer available)? Thanks

Reply
KNXperts
Ensign KNXperts
Ensign

Posted: ‎2025-09-15 11:46 AM

0 Likes
0
3215
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-15 11:46 AM

Hello again Heribert,

 

I can confirm that the https link with the clear cache is also not working. We have the same result, a white blank page. The http server in the wiser is set to http and https. And if it was a link or security issue, why would we see the scheduler and the trends? So I think it's a compatibility issue. How can we safely downgrade the server? And will the new app be compatible with the firmware 2.7 of the wiser?

 

Thanks.

Reply
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
Janeway

Posted: ‎2025-09-16 10:14 PM . Last Modified: ‎2025-09-16 10:27 PM

0 Likes
0
3200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-16 10:14 PM

@KNXperts 


Downgrade is not supported, only way to do that is flash the SD card with bootloader and select old FW when asked to upload the FW.

 

See this application note / guide:

https://www.se.com/hk/en/download/document/AN2_001/

 

Make sure to have a backup as all content will be erased from the card, the backup needs to be from same version or older version then the FW you will restore, if your current backup is in version 3.0 and you use an older FW you cannot restore the higher version backup, so keep that in mind before you start walking this route…

 

Firmware for the new app needs to be at least 3.0

 

See: https://www.productinfo.schneider-electric.com/wiser-knx/

 

IMG_4985.jpeg

So if you roll back to an older FW you can only use the browser or something like the Kibro App

Reply
KNXperts
Ensign KNXperts
Ensign

Posted: ‎2025-09-18 01:51 PM

0 Likes
0
3156
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-18 01:51 PM

We have finally downgraded the wiser to version 2.7.0, the version which the old wiser was working perfectly with the umotion touch panels, but now we have another issue. When we open the touch3 app on the browser, we get the following error:
 
3.png
We suspect because the backup we restored from had a more recent version of the touch3 app. So when we try to update it now, we also get an error:
 

 

1.png2.png

  

 

 

 
We also have the same error when we try to update or install any app. Seing the online forums, I saw it can be due that the wiser is on an outdated firmware version (2.7.0) which we need for the touch panels to work.
 
I saw that there was a way to install an app by upload the package. Is it possible to fix this error somehow or provide me with the touch3 app package file (preferable pre 3.18.7) and the cloud connector package as well to see if the cloud connection still works with the old app (wiser for knx).
Reply
KNXperts
Ensign KNXperts
Ensign

Posted: ‎2025-09-23 10:56 AM

0 Likes
0
3065
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-23 10:56 AM

Hi,

 

Suggestions anyone?

 

Thanks.

Reply
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
Janeway

Posted: ‎2025-09-24 09:42 PM

0 Likes
1
3046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-24 09:42 PM

@Thomas_Rohde

 

I have seen this error before, but it's so long ago i cannot remember what the cause was, was there a .lmup created for this? Do you remember? I search my history but can't find anything..

Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2025-09-26 02:26 AM

0 Likes
0
3000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-26 02:26 AM

Hi Erwin!
David is looking for this topic directly with the customer.
But still,"bedankt" for the hint.


Kind regards
Thomas

Application Design Engineer
Reply
David_Navratil
Lt. Commander David_Navratil Lt. Commander
Lt. Commander

Posted: ‎2025-09-29 01:40 AM

0 Likes
0
2942
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-29 01:40 AM

Hello,

Seems like backup you have is created on later version of Touch then you restore it on and it is probably the rootcause of the error line you get.

Can you try right now delete whole Touch visualization and manually create one widget and check if the error message is still there?

If this does not help can you try also flash the SD card again and without backup just create KNX object and one Widget?

I understand this is not good approach and it is huge effort to make it manually but I am worried in such a case we have no choise. This is highly unsupported FW version and Touch version from controller point of view.

 

Kind regards

David

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore