Dear Sir,
I am Prabhu francis from Singapore.
For current project we are using KNX RF sensor in office. Client requirement to lock the sensor function at 8am to 6am Lights remain always ON.Usually we prefer MTN630919 which easily done locking function and scheduling on Spacelynk.
Right now we are using different type of sensor which could not make it. We have already done in scripting-resident based works fine. But we see the option in automations we already done the settingt but it doesnot execute.
I have attached image screenshot whether i am making any mismatch of the program?
Regards,
Prabhu Francis
Link copied. Please paste this link to share this article on your social media post.
There is no attachment and i have 1 super tip..
Just use SE sensors that does not introduce your issue ๐ and stay away from the brand you try to use now ๐
Link copied. Please paste this link to share this article on your social media post.
For sure automations could help you out here, but why taking this detour when it can be done with a super small 5 line script for all your sensors?
Just create your motion inputs in range xx/1/xxx and your motion output objects in xx/2/xxx and attach to each Motion input object the TAG "Motion" and create a event based script attached to this TAG..
And insert this script:
This script will be triggered by any of your motion sensors input object (in range xx/1/xxx), checks if the lock (scheduler) is disabled and sends it's current value to the output object (in range xx/2/xxx), when the lock is enabled it does nothing with the input.
This is way simpler then creating an automation for each and every motion sensor...
Link copied. Please paste this link to share this article on your social media post.
There is no attachment and i have 1 super tip..
Just use SE sensors that does not introduce your issue ๐ and stay away from the brand you try to use now ๐
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Most we use prefer wired KNX we use MTN630919..Unfornutualy we are using wireless KNX RF that why we some issue on paramaters.
Link copied. Please paste this link to share this article on your social media post.
For sure automations could help you out here, but why taking this detour when it can be done with a super small 5 line script for all your sensors?
Just create your motion inputs in range xx/1/xxx and your motion output objects in xx/2/xxx and attach to each Motion input object the TAG "Motion" and create a event based script attached to this TAG..
And insert this script:
This script will be triggered by any of your motion sensors input object (in range xx/1/xxx), checks if the lock (scheduler) is disabled and sends it's current value to the output object (in range xx/2/xxx), when the lock is enabled it does nothing with the input.
This is way simpler then creating an automation for each and every motion sensor...