Master/Slave DALI motion sensor on MTN6725-0101

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • Master/Slave DALI motion sensor on MTN6725-0101
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to SpaceLogic KNX Forum
Start a Topic
sesa138580_brid
sesa138580_brid Cadet
Cadet

Posted: ‎2025-09-17 11:22 AM

1 Like
5
790
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-17 11:22 AM

Master/Slave DALI motion sensor on MTN6725-0101

Hi

I can not find any documentation of how to configure DALI motion sersors as Master/Slave.

Does anyone have a KNX project with 2 or more DALI motion sensor are used as Master/Slave?

Or do any have some instructions how to setup the one as master an how to setup the last as slaves?

 

 

Labels
  • Labels:
  • Documents
  • SpaceLogic devices
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
KNXJensen
Ensign KNXJensen
Ensign

Posted: ‎2025-09-18 04:26 AM

0 Likes
0
758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-18 04:26 AM

Hi everyone,

I’m currently trying to set up a DALI sensor with the Master/Slave function. Unfortunately, the manual only provides a very brief description, and the e-learning course doesn’t really cover this topic either.

I was wondering if anyone here has some experience with this setup and could share some insights, best practices, or even example configurations.

Thanks in advance for your help!

Reply
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
Janeway

Posted: ‎2025-09-18 10:26 PM . Last Modified: ‎2025-09-18 10:43 PM

2 Likes
2
739
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-18 10:26 PM

@KNXJensen @sesa138580_brid 

 

Have you tried to enable the External Presence on the master sensor (MB1 in this case)?

ErwinvdZwart_0-1758259100283.png

And then link the objects from the slave(s) (MB2 + MB3 in this case)

 

ErwinvdZwart_1-1758259175322.png

ErwinvdZwart_5-1758259553073.png

 

to the external object of the master

 

ErwinvdZwart_2-1758259213957.png

 

and link the switching object of your master to your light source input

 

ErwinvdZwart_3-1758259451307.png

ErwinvdZwart_4-1758259477134.png

 

I would set the delay of the slaves relative short, or at least shorter then the time of the master to avoid that the master is done with the switching but the slave is still in countdown before sending the new movement.

 

ErwinvdZwart_6-1758259771705.png

 

See sample project in the attachment (not tested as i don't have 2 sensors)

Attachments
DALI Master Slave Test.zip
Reply
KNXJensen
Ensign KNXJensen
Ensign

Posted: ‎2025-09-19 12:44 AM

0 Likes
1
725
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-19 12:44 AM

KNXJensen_1-1758267458716.png

Hi Erwin 

This is not my project. I’m working on behalf of an installer who carried out the work, but he’s having trouble getting it to run properly, so I’m assisting him.

The installer plans to change the application from 7311/2.0 to 7311/2.1 and will check how it works.
He will also set up the master PIR and slave PIR as suggested, and verify that the slave operates at half the time of the master.

He will get back to me once the testing is done.

Best regards,
Tommi

 

Reply
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
Janeway

Posted: ‎2025-09-19 04:12 AM . Last Modified: ‎2025-09-19 04:14 AM

1 Like
0
719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-19 04:12 AM

@KNXJensen 

 

Hi Tommi, did not linked the username to you (: 

 

Let me know if you need additional help, but should work..

 

PS: As old PAE you should have known this (:

Reply
KNXJensen
Ensign KNXJensen
Ensign

Posted: ‎2025-09-28 08:34 AM

1 Like
0
637
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-28 08:34 AM

Hi Erwin,

I haven’t been on site myself; I’ve only communicated with the customer.
Yes, I already mentioned the points you suggested, but I just wanted to check if there were any other options beyond the obvious ones.

The customer has tested the settings now, and everything is working.

Thanks a lot for your help!

Best regards,
Tommi

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore