Hi,
Can I connect th spacelynk "directly" to an Enterprise Server having the spacelynk as an BBMD???
As always thanks for your support,
Regards
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
If they are in the same LAN you don’t need BBMD, just give each SL a unique instance ID and discover them in any AS-P or ES..
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
No, SL is a BACnet server that can
subscribe to a BBMD as a foreign device, but why don’t you enable the BBMD in the ES BACnet interface if you need one?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
I understand; so intead of building something like the picture below, I just "connect" the SL directly to the ES, if the are in the same segment (VLAN or LAN), is that correct?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
If they are in the same LAN you don’t need BBMD, just give each SL a unique instance ID and discover them in any AS-P or ES..