HI,
Fairly new to the SpaceLYnk so apologies if this is a silly question but I can't seem to find the answer.
What is the Default Network ID on the SpaceLynk and is it possible to change this to a new number. I can see where the Device ID can be changed but not the Network ID.
Thanks
Link copied. Please paste this link to share this article on your social media post.
Hi AndyRolly,
BACnet network numbers are assigned within BACnet router.
spaceLYnk is not a router, so this isn’t a property on this device.
Link copied. Please paste this link to share this article on your social media post.
In Niagara this is known as the Network number. It can be between 1 and 65,534.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Thank you - that makes sense as the Jace is.