Schneider SL&HL no action Iphone bug

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • Schneider SL&HL no action Iphone bug
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Related Products
product field
SpaceLogic KNX - 4ʺ Touch Unit
product field
KNX Push Button Dynamic Labeling, universal
product field
Wiser for KNX : logic controller

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Start a Topic
Solved
domotiqa
Lt. Commander domotiqa
Lt. Commander

Posted: ‎2019-06-08 08:33 AM . Last Modified: ‎2024-07-14 11:49 PM

0 Likes
7
929
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-06-08 08:33 AM

Schneider SL&HL no action Iphone bug

Hello,

I have a customer who recently has a bug in Touch/mosaic that suddendly appear (maybe after a IOS update) !

First we use HL with 2.3.0 firmware.

The bug occur on both Iphone of the husband and wife customer (iphone 6smax and IOS 12.3.1).

The bug look like the https issue with safari, but is not !

I tried with logic machine applestore software, with SE Wiser for knx, with SAFARI http direct access, and with Chrome also ! I clear SAFARI cache and restart Iphone !


the customer can access the Touch visualisation, go in a room, but when he click on a Light, no action !

For me, It work on a computer and with my personal Iphone (12.3.0 IOS), but not with their Iphone !


Any help appreciate !

Smarthome & Smartbuilding Expert
  • Thumbnail of SpaceLogic KNX - 4ʺ Touch Unit
    SpaceLogic KNX - 4ʺ Touch Unit
  • Thumbnail of KNX Push Button Dynamic Labeling, universal
    KNX Push Button Dynamic Labeling, universal
  • Thumbnail of Wiser for KNX : logic controller
    Wiser for KNX : logic controller
View products (3)
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2019-09-19 10:49 PM

0 Likes
5
905
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-09-19 10:49 PM

Hello contact_domotiq,

 

any news on your topic?

 

Kind regards
Thomas

Kind regards
Thomas

Application Design Engineer

See Answer In Context

Reply
Replies 7
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2019-08-14 06:12 AM

0 Likes
6
912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-14 06:12 AM

Hello,

 

this is really strange because I privately use it as well and have not faced this issue yet.

I had the same constellation (iOS+W4K FW-Version). Are you sure that you have a WiFi-Connection at this moment?

 

Do you face still the same behaviour after update to W4K 2.4 and iOS 12.4?

 

Kind regards

Thomas Rohde

Kind regards
Thomas

Application Design Engineer
Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2019-09-19 10:49 PM

0 Likes
5
906
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-09-19 10:49 PM

Hello contact_domotiq,

 

any news on your topic?

 

Kind regards
Thomas

Kind regards
Thomas

Application Design Engineer
Reply
domotiqa
Lt. Commander domotiqa
Lt. Commander

Posted: ‎2020-01-22 05:37 AM

1 Like
4
896
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-01-22 05:37 AM

This was Cache problem. Needed to go Iphone date to 2030. Load app, then go back to normal date

Smarthome & Smartbuilding Expert
Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2020-01-22 05:40 AM

0 Likes
0
894
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-01-22 05:40 AM

Thanks a lot for the feedback!

Kind regards
Thomas

Application Design Engineer
Reply
Anonymous user
Not applicable

Posted: ‎2020-01-22 11:20 PM

0 Likes
2
891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-01-22 11:20 PM

Hello

 

I'm from Italian TSC for KNX Support; an Italian customer have the same problem, could you please explain what is exactly the procedure about date?

Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2020-01-22 11:52 PM

1 Like
1
889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-01-22 11:52 PM

Hi, I have currently no concrete idea why a change of a date is bringing the needed solution instead of deleting the cache competley but maybe I am not familar enough with this kind of technology.

 

As specially by reading this example from google and I guess iOS works similar: 

As an example of such an archive created by the search engines, the archive of the search engine most commonly used in Germany, the so-called Google cache, will be explained here.
Google takes a screenshot for each URL that has been included in the search engine index as a backup in the event that the current website is not available. This snapshot is then saved in the Google cache. Accordingly, the Google cache acts as a virtual archive. If the website you are looking for cannot be opened or can only be opened very slowly, the page can be called up from the cache instead. Google points out the date and time of the screenshot.

 

Maybe due to the change of date to 2030 and back the system identifies the screenshot as somehow not actual and creates a new one?! => Just guessing!

 

By deactivating the automatical time synchronisation you can manually adapt the date.
Try to call the Visu again with this incorrect date.

Set back the date settings and try to call the dedicated page again.

 

Please let us know if this was solving the issue by your client.

 

 

 

 

Kind regards
Thomas

Application Design Engineer
Reply
domotiqa
Lt. Commander domotiqa
Lt. Commander

Posted: ‎2020-01-23 12:48 PM

2 Likes
0
884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-01-23 12:48 PM

You go to Iphone settings, and change date in Iphone to a futur date (1 year later for example).

Try clearing cache from safari settings also, install last Ios update and reboot.

 

Change date to Iphone to Automatic, then reload the HL/SL website

 

solved for me

Smarthome & Smartbuilding Expert
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore