Latest version of Google Chrome Browser (80.0.3987.106) breaks interfaces configuration window.
FF 72.0.2 is ok
As the same behavior has been identified in dev version of Google Chrome we are working fix the issue.
Please, use older version of Chrome for IP settings or different browser.
Note: as a workaround please press F12 key (2x). This re-render the page.
Update (20200408) - Google has released Chrome version 81.0.4044.92 on 7/4/2020 which fixes the problem, without the bugfix patch.
Link copied. Please paste this link to share this article on your social media post.
Dear all,
the topic is solved by adding this little patch-file to the dedicated controller.
It is distributed as *.lmup file attached to this post. Please, clean browser's cache after patch.
Below you will find the steps as a reminder ๐
Link copied. Please paste this link to share this article on your social media post.
Hi Petr,
I faced the same issue in Admin password change page after a hardware reset. I couldn't set the password in chrome, I had to go to another browser to set the password.
Thanks,
Mahmoud
Link copied. Please paste this link to share this article on your social media post.
Yes, correct. It is same dialogue window. F12 works as well in this case, but this is more annoying because customer see empty window when he grabs a fresh new product.
Other configuration windows from system page seems work. Let's see where is the root cause.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Dear all,
the topic is solved by adding this little patch-file to the dedicated controller.
It is distributed as *.lmup file attached to this post. Please, clean browser's cache after patch.
Below you will find the steps as a reminder ๐