Multitouch Pro Error 0008 (KNX)

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • Multitouch Pro Error 0008 (KNX)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to SpaceLogic KNX Forum
Start a Topic
Anonymous user
Not applicable

Posted: ‎2022-06-01 06:29 AM . Last Modified: ‎2022-06-28 04:02 AM

1 Like
13
6055
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-01 06:29 AM

Multitouch Pro Error 0008 (KNX)

I downloaded the Individual address for Multitouch Pro (MTN6215-5910)and it is done easily.

Afterwhile, I try to download The application but ETS never recognise the device (only this one among the other 12), I try to unload the individual address but it is still never recognized (Although I did click the programming button).

Later on, the device screen converted from ( no config) to (wait bus...) as you see in the picture, also after waiting a while the Red screen appear with Error 0008. 

Can anyone help me how to fix this issue?

Attachments
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 13
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2022-06-01 07:49 AM

0 Likes
7
6027
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-01 07:49 AM

Hello Mobaet

 

Error 0008 indicates an internal communication problem between the two microcontrollers.

 

Some months ago i had a similar case when this error was shown after device unload.

 

The problem was solved by disconnecting the module from the KNX TP bus, and then connecting it to a PC through its USB port. After PC recognized the USB storage, we simply disconnected the module from the PC, re-attached it to the KNX Bus, and we were able to download application to it.

 

Hope this helps in your case, too.

Tags (1)
  • Tags:
  • english
Reply
Anonymous user
Not applicable

Posted: ‎2022-06-01 08:57 AM

0 Likes
1
6017
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-01 08:57 AM

Hello,

Thank you for your answer.

Actually, I did that but it did not work at all. I have attempted to update the firmware but it did not work because no firmware button is possible to reach. When connect to a PC, it is recognized by the PC as storage so it is a good sign.

Tags (1)
  • Tags:
  • english
Reply
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2022-06-02 01:08 AM

0 Likes
0
5994
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-02 01:08 AM

Hello

Yes correct, to be able to do firmware update You need to activate update button in ETS and download application. But from your picture I could see that Your device is having latest firmware version 26.1.

Tags (1)
  • Tags:
  • english
Reply
c.molk
c.molk
Cadet

Posted: ‎2024-01-29 05:38 AM

0 Likes
1
4446
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-29 05:38 AM

Dear Mr. Dölger,

I have the same problem: I can assign the physical address to the device (Multitouch MTN6215-5910), but cannt program it. When  connecting to a PC "USB DEVICE MSC MODE" is shown on the Multitouch, but the PC dont recognize the USB storage on the Multitouch. Different multitouches are displayed in ETS 6: System M, System Design with different Version number (1.1 and 1.4). Unfortunately, the label on the back of the device does not provide any information about whether it is "M" or "Design" or which version number. There is only the number "3220 0D" What can I do? The device may be defective?

 

 

Reply
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2024-01-30 01:48 AM

0 Likes
0
4391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-30 01:48 AM

Dear C.Molk

As you mention MTN6215-5910, this is Multitouch Pro System Design (System-M device has product number MTN6215-0310).

 

You need to select the ETS application depending on the firmware on the device, firmware version is shortly shown when powering the device.

 

The number on the backside is the date code and version. Your device is from February 2023 and due to that most probably has firmware 30.7. For this firmware you should select application for System Design version 1.4.

 

If you still are not able to download ETS application I would need to know what error message ETS is throwing. That would give more hint why the download is failing.

Reply
vFix
vFix
Cadet

Posted: ‎2024-09-10 07:58 PM

0 Likes
0
3659
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-10 07:58 PM

Dear Mr. Dölger,

I have the same problem. Error code 0008 some time after WAIT BUS...
The solution you proposed - connecting only via USB and then only via TP does not lead to a result (as the disk device is detected and the files are visible). The screen is black, when you press the Program mode button, the red LED lights up, but the physitial address is not recording. Also, in ETS, in diagnostics, when starting device search in programming mode, no devices are displayed. I have MTN6215-5910 FS12 FW26.3 CV27. I started updating FW due to the fact that an error related to the EEPROM (not configured) appeared. I started the first step - in ETS, I activated the window display option for updating FW and started downloading the application, but it ended with an error and after that a black screen when connected via TP. Later I noticed that I was downloading from version 1.4, and the panel seemed to be configured from version 1.1...
I would really appreciate your help!

Roman

Reply
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2024-09-12 04:40 AM

0 Likes
0
3615
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-12 04:40 AM

Hello

There is to consider the compatibility between firmware and ETS application. When using ETS application 1.1 you need to use firmware 25.3 or lower. When using higher FW versions you need to use ETS application 1.4. For FW you also need to consider which design version you have, either System-M (MTN6215-0310) or System-D (MTN6215-5910). For each version there is different firmware.

When your device now is having FW 26.3 you should be able to program it with application 1.4 even it was programmed with 1.1 before. But when trying to download with application 1.1 it won't work.

 

Reply
vFix
vFix
Cadet

Posted: ‎2024-09-13 02:15 AM

0 Likes
0
3592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-13 02:15 AM

I have a SystemD (MTN6215-5910) on which FW 26.3 was originally installed. After an unsuccessful download of the 1.4 application from ETS, the screen is now black and nothing can be done with it from the TP side, when the programm mode button is pressed, the red LED lights up, but ETS does not see this, neither when loading the address nor through the search for programming mode devices. When connected only via USB, the computer sees the panel as a disk. When connected via USB and TP, the WAIT BUS label appears first.. and after a while, Error 0008..

Reply
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2024-09-13 06:08 AM

0 Likes
0
3558
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-13 06:08 AM

That indeed looks like the device is defective. It seems not to be able to communicate via TP. Could be a defective component or microcontroller; or the communication between the two microcontrollers. In case it is the connection between the microcontrollers you might open the device and check if the two PCBAs are properly connected. If also this does not help I guess you need a new device.

Reply
Abdulrhman23
Abdulrhman23 Cadet | EcoXpert Master
Cadet | EcoXpert Master

Posted: ‎2024-12-11 03:32 PM

0 Likes
2
3067
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-11 03:32 PM

Abdulrhman23_0-1733959860353.png

What is the solution to this problem please?

 

 

Reply
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2024-12-12 12:24 AM

0 Likes
1
3054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-12 12:24 AM

Hello Abdulrhman23

Error 0040 indicates a problem with the analogue input which is the connector where you could connect an external temperature sensor. Seems the product is defective.

Reply
cristianbriscu
cristianbriscu
Cadet

Posted: ‎2025-02-15 08:32 AM

0 Likes
0
2577
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-15 08:32 AM

Hello, I also have one like that, with error 0040, it is getting connected to ETS and address assgined, also configuration done on it. But it still displays the error. It was bought from a german retailer and shipped to Romania, is the any way that I can exchange it here in Romania? 

Reply
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2025-03-03 01:44 AM

0 Likes
0
2485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-03 01:44 AM

I guess you need to contact the seller in Germany. But I am not a specialist in respect of sales. 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore