MTN6500-0103 IP Router KNX Communication Issue

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • MTN6500-0103 IP Router KNX Communication Issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Start a Topic
Solved
ErkinV
Lieutenant | EcoXpert Master ErkinV Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2025-04-25 05:16 AM . Last Modified: ‎2025-04-25 06:52 AM

0 Likes
10
4717
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-04-25 05:16 AM

MTN6500-0103 IP Router KNX Communication Issue

Hello everyone, I have a question and wanted to illustrate it with a drawing to explain it better.

 

As shown in the first image, I have a line with an IP router and 63 devices connected underneath. The addressing on this line is also configured accordingly. Since we were experiencing some telegram transmission issues, we added a new-generation router in between, as shown in the second image.

 

However, when we connect the CAT-6 communication cable, the KNX LED on the field device starts flashing red continuously, and none of the devices on the line become reachable. it essentially locks the entire line. Interestingly, when I disconnect the building's switch and instead plug in a CAT-6 cable from my own computer, the issue disappears completely. You can also see this behavior in the videos.

 

Here are my questions:

 

- Other than the address of the newly added device, all the devices connected underneath still have the same addresses. Could this cause a problem?

 

- Is there a security feature on the new device that we are unaware of and need to activate?

 

We need to urgently get back to our client regarding this issue, so I would really appreciate your support.

 

Thanks in advance to everyone!

 

 

@Thomas_Rohde

@Erwin-vd-Zwart 

@Heribert_Dölger 

Attachments
Labels
  • Labels:
  • Protocols
  • SpaceLYnk
  • Wiser for KNX
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2025-05-23 01:01 AM

1 Like
0
4391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-23 01:01 AM

Hello ErkinV!
If I would be in your shoes, I would try to seperate (if somehow possible) the complete KNX IP-Network from the given IT-Installation.

Just for a test.

Means to use a simple router/switch which you trust and where you have good experience with.
If the installation is then working properly as you expect, I would ask the IT guys why is it working within your local test setup but not at all in the real installation.


I guess they have a manageable router/switch which is somehow blocking parts.

 

Kind regards
Thomas

Application Design Engineer

See Answer In Context

Reply
Replies 10
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2025-04-25 07:59 AM

1 Like
1
4689
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-04-25 07:59 AM

Hello ErkinV

 

You cannot implement an IP router in the subline of another router or coupler, and especially not with an address that does not match to this line. Question would be whether the devices in the subline of IP router 5.1.0 are still connected as well to line with router 1.10.0.

 

IP Routers should share the same main line, in this case the IP Line. The addresses of the Routers should be in the same Domain. So if the first one is 1.10.0 the other one could be 1.11.0. But then all devices connected to router 1.11.0 must have addresses from 1.11.1 … 1.11.63. And of Course there no direct bus Connection between both lines and you would Need another KNX power supply for line 11.1.

 

In General, I think this solution approach is not the best. As you Mention communication Problems it would be better to analyse why those communication Problems appear. If it is a matter of wiring length or insufficient power supply it would be better to install a coupler in the middle of line 1.10 and configure it as a repeater (with address 1.10.64). The other devices in this line then could Keep their address. But you would then need an additional KNX power supply for this new Segment.

 

Is the shown line the complete network or are there additional lines in the Project? If this is the whole network you would not Need a router at all, maybe only the interface function to get Access to the network from ETS.

 

The blinking of KNX LED at the router indiates Transmission Errors but could be minor Errors like missing acknowledgements or repeat telegrams. I Guess the blinking stops because with ETS connected the acknowledgements will come from ETS.

Reply
ErkinV
Lieutenant | EcoXpert Master ErkinV Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2025-04-29 11:11 PM

0 Likes
0
4610
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-04-29 11:11 PM

Hi Heribert,

 

In the first screenshot from ETS, you can see the topology. I marked the split line in red, and the newly added router on that line is marked in green. In the second screenshot, the devices from the red line are physically connected in the field to the newly added router (the green line).

What I would like to ask is: should I move the devices in the red area (from the second screenshot) under the new router with the address 5.1.0, and also update their addresses accordingly? Is this the correct approach?

Attachments
Reply
Cristiano_Carli_Ballola
Lt. Commander Cristiano_Carli_Ballola Lt. Commander
Lt. Commander

Posted: ‎2025-04-30 12:21 AM

1 Like
3
4604
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-04-30 12:21 AM

Hello ErkinV,

Regardless of where the devices are currently installed or will be moved, what you absolutely need to do is change the parameters of the IP routers by setting filtering according to the filter tables calculated by ETS.
If you leave the communication on "Route", all telegrams of the whole project, which appears to be quite large, will pass through each line, causing a huge traffic communication, which could be the cause of the issues you complain about.

Reply
ErkinV
Lieutenant | EcoXpert Master ErkinV Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2025-04-30 04:29 AM

0 Likes
2
4598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-04-30 04:29 AM

Hi Cristiano,

 

I'm asking to clarify something I'm not sure about — you're suggesting that it would be better to set all the attached configurations to "filter," right? I also have different routers used in this project. If I change them all to "filter," would it help ease the data traffic? As you mentioned, apart from the issue in the subject line, I'm also experiencing some lags in data traffic as you described.

Attachments
Reply
Cristiano_Carli_Ballola
Lt. Commander Cristiano_Carli_Ballola Lt. Commander
Lt. Commander

Posted: ‎2025-05-05 11:18 PM

1 Like
1
4572
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-05 11:18 PM

Yes sir!
It's more than suggested, it's mandatory.
This is the main purpose of any KNX coupler, handle the telegrams traffic within the line they belong to.
They are equipped with the so called filter table, in which are inserted all the group address telegrams that need to be forwarded through their designated KNX bus line.
The filter table is automatically generated by ETS according to your project configuration.
Bypassing the filter table means, for most telegrams, tripling traffic!

Reply
ErkinV
Lieutenant | EcoXpert Master ErkinV Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2025-05-06 04:11 AM

0 Likes
0
4558
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-06 04:11 AM

Hi Cristiano,

As indicated, I have arranged the addresses according to the device topology and sorted them based on the IP Router. I also configured all the routers with the filter settings and uploaded the configurations.

However, when I connected the CAT data cable of this new device to the system backbone and tested it, I experienced issues with the other data: devices stopped working and there were disruptions in the scenarios.

Is there another approach or test I should try to solve this issue? I also added an additional power supply to the router to prevent bus voltage drops, but I still encountered problems in the system.

Please find the addresses attached. 😞

Attachments
Reply
Cristiano_Carli_Ballola
Lt. Commander Cristiano_Carli_Ballola Lt. Commander
Lt. Commander

Posted: ‎2025-05-06 11:32 PM

0 Likes
1
4543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-06 11:32 PM

Hi @ErkinV ,

using ETS you are you able to monitor and record the data traffic within the KNX Bus line and the KNX IP line.
By analyzing the recording you should be able to verify if the telegrams are routed correctly between different lines and/or areas.
The communication on KNX/IP takes place in Multicast mode; check with the support of the IT manager that the switches/routers of the network infrastructure have been set up correctly for this to happen

Reply
ErkinV
Lieutenant | EcoXpert Master ErkinV Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2025-05-13 07:28 AM

0 Likes
0
4478
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-13 07:28 AM

Hi Cristiano,
I spoke with someone from IT, but they keep insisting that everything looks fine when they check it. How can I prove otherwise? How can I perform the task you mentioned in the program?
Would it be possible for you to explain it to me, perhaps with an image or a video?

Reply
ErkinV
Lieutenant | EcoXpert Master ErkinV Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2025-05-22 11:21 PM

0 Likes
0
4403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-22 11:21 PM

"Hi, could you please help me with this matter?"

 

@Thomas_Rohde

 

Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2025-05-23 01:01 AM

1 Like
0
4392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-23 01:01 AM

Hello ErkinV!
If I would be in your shoes, I would try to seperate (if somehow possible) the complete KNX IP-Network from the given IT-Installation.

Just for a test.

Means to use a simple router/switch which you trust and where you have good experience with.
If the installation is then working properly as you expect, I would ask the IT guys why is it working within your local test setup but not at all in the real installation.


I guess they have a manageable router/switch which is somehow blocking parts.

 

Kind regards
Thomas

Application Design Engineer
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.