LSS100300 Spacelogic KNX BMS Gateway shows incorrect status of devices after startup or power failure

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • LSS100300 Spacelogic KNX BMS Gateway shows incorrect status of devices after startup or power failure
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Start a Topic
Solved
ranla
Lieutenant | EcoXpert Master ranla Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-07-11 04:11 AM . Last Modified: ‎2024-07-14 11:38 PM

0 Likes
3
1073
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-11 04:11 AM

LSS100300 Spacelogic KNX BMS Gateway shows incorrect status of devices after startup or power failure

Hi,

 

We started using the Spacelogic KNX BMS IP Gateway (LSS100300) about a year ago, instead of the Spacelynk gateway (LSS100200) in our projects that only require sending knx data to Ecostruxure Builiding Operation devices via bacnet/IP without graphics.

 

However, there is a feature that exists in the spacelynk device, that doesn't seem to exist in the BMS gateway and is creating big issues for us.

 

In the Spacelynk device, there is an option to tick in the group address settings "read on startup".

So basically if the device  itself restarts for some reason, or if there is a temporary power  failure, upon startup it reads the correct status of the KNX devices group addressees that were selected to be read, and displays the correct status, also on the bacnet server.

 

This option doesn't seem to exist in the BMS gateway, and several clients have pointed this issue to us, that the status isn't correctly displayed

 

Is there any plan to implement this ? 

 

we need a solution.

 

Thanks,

 

Ron

Labels
  • Labels:
  • Protocols
  • SpaceLogic devices
  • SpaceLYnk
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
Janeway

Posted: ‎2024-07-12 02:57 AM

2 Likes
1
1013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-12 02:57 AM

The LSS100300 is a gateway and not a controller, so what it does is exactly what you might expect from it, it transfer KNX <-> BACnet without any additional actions.

 

When a KNX telegram is missed due to a system failure the telegram has to be send again, that is why cyclic sending exists.

 

If you need a device to execute read request you need a controller and not a gateway, due to this additional functionality you need a more expensive device (controller)

See Answer In Context

Reply
Replies 3
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
Janeway

Posted: ‎2024-07-12 02:57 AM

2 Likes
1
1014
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-12 02:57 AM

The LSS100300 is a gateway and not a controller, so what it does is exactly what you might expect from it, it transfer KNX <-> BACnet without any additional actions.

 

When a KNX telegram is missed due to a system failure the telegram has to be send again, that is why cyclic sending exists.

 

If you need a device to execute read request you need a controller and not a gateway, due to this additional functionality you need a more expensive device (controller)

Reply
ranla
Lieutenant | EcoXpert Master ranla Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-07-15 07:14 AM

0 Likes
0
966
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-15 07:14 AM

Hi Erwin,

 

Thanks for the quick response.

I understand what your are saying, however it doesn't seem right that if the gateway has some kind of failure, it can't execute some type of read operation on startup.

I dont think this is a functionality that is expected only from a controller.

 

The solution of sending hundreds of telegrams cyclicly on the bus every few minutes when all we need is 1 read on startup is a bit of an overkill, and will just congest the bus.

 

We would appreciate you considering adding this feature in future firmware updates if possible.

Reply
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
Janeway

Posted: ‎2024-07-15 10:42 PM . Last Modified: ‎2024-07-15 10:51 PM

0 Likes
0
950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-15 10:42 PM

Any action other then passing data from A <-> B is taking control, hence controller functionality, i already asked R&D as i agree that it could make sense, first reaction was same as mine, you need a controller and not a gateway when you want to execute control actions.

 

If you compare it with any other gateway (Modbus/BACnet/DMX or likewise) you face the same issue, a gateway never perform actions by itself.

 

Same counts for KNX IP routers, when a KNX IP router is down for whatever reason it won't perform read requests on startup so you will have same issue in that KNX segment. You could consider backup solutions like a panel UPS to avoid downtime of a gateway.

 

Otherwise your solution is known, use a SL controller instead of a gateway.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore