KNX communication

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • KNX communication
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Related Products
product field
SpaceLogic KNX - 4ʺ Touch Unit
product field
KNX Push Button Dynamic Labeling, universal
product field
Wiser for KNX : logic controller

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Start a Topic
Solved
AmrMustafa
Ensign AmrMustafa
Ensign

Posted: ‎2022-02-01 05:13 AM . Last Modified: ‎2024-07-14 11:45 PM

1 Like
4
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-01 05:13 AM

KNX communication

Hi

I have 35 panels on every 35 floor 
every panel has a KNX product And Connect with KNX field devices and every panel Has (wiser 100100)
each panel connected separately with the product on the same floor and each Wiser 100100 connected to the nearest datapoint 

how can I control and see all 35 Panels in this case?

if I changed the topology of knx Bus can I use wiser 100100 as an IP router Gateway or not? if yes (HOW?)


if anyone has a solution please advise me?

  • Thumbnail of SpaceLogic KNX - 4ʺ Touch Unit
    SpaceLogic KNX - 4ʺ Touch Unit
  • Thumbnail of KNX Push Button Dynamic Labeling, universal
    KNX Push Button Dynamic Labeling, universal
  • Thumbnail of Wiser for KNX : logic controller
    Wiser for KNX : logic controller
View products (3)
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2022-02-03 02:32 AM . Last Modified: ‎2022-02-03 02:34 AM

0 Likes
1
1237
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-03 02:32 AM

Hello AmrMustafa,

 

To "if I connected all of panel to internet ( how much conflict between Group address for each panel )"

I guess that all floors have the same structure and does not need to communicate to each other from KNX-Point of view.
2022-02-03_10h26_15.png

If this is the case then you can select "TP-UART". If you are fully sure that you didnt want any KNX-IP-Features (use it as an interface) then you can untick the dedicated parameter.
can simply deactivate the KNX-Communication on IP-Side. Means each KNX-Communicationstays on the dedicated level/floor.

2022-02-03_11h09_01.png

If this is set you can still have the W4K connected to the internet to get for example the actual time which is needed for sunrise/sunset features.


To "I ask if I want to  control all panels from 1 workstation  how that ?"

You can create, just as one example, in the first W4K a custom visualization where you can integrate all 34 views of the TouchVisu. For that you need to create the dedicated structure to navigate between the different floors.
Each W4K (of each floor) needs to be included in a dedicated "Frame". Here you enter the dedicated URL of the TouchVisu of each W4K within the building.

 

 

Here you find the link to the dedicated manual to review all instructions more in detail.
https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=Wiser+for+KNX+%28LS... 

 

 

Kind regards
Thomas

Application Design Engineer

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2022-02-03 02:36 AM

0 Likes
0
1235
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-03 02:36 AM

This picture belongs to the threat above within the section with the "Frame".
For some reasons I couldnt add it there.

2022-02-03_11h25_31.png

 


sorry for that

 

Kind regards
Thomas

Application Design Engineer

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 4
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2022-02-02 01:51 AM

0 Likes
3
1248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-02 01:51 AM

Hello AmrMustafa,

 

to "how can I control and see all 35 Panels in this case?"
I am not sure that I get this question fully. Normally, when all W4K are connected to a network than you could control all of them by entering the dedicated IP of W4K to reach the visu?! Please be more specific.

 

to "if I changed the topology of knx Bus can I use wiser 100100 as an IP router Gateway or not?"
Means you have currently a KNX Backbone with line coupler and you are thinking to change to an IP-Backbone?
Is it that what you are looking for?

Kind regards
Thomas

Application Design Engineer
Tags (1)
  • Tags:
  • english
Reply
AmrMustafa
Ensign AmrMustafa
Ensign

Posted: ‎2022-02-02 04:28 AM

0 Likes
2
1245
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-02 04:28 AM

Hi,Thomas
No, no line coupler & no bus coupler it is just only LS100100 

all 34 panel contain ( powersupply , actuator , sensor , wiser ls100100) for one floor 

I ask if I want to  control all panels from 1 workstation  how that ?
if I connected all of panel to internet ( how much conflict between Group address for each panel )

is there another way ? 

Tags (1)
  • Tags:
  • english
Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2022-02-03 02:32 AM . Last Modified: ‎2022-02-03 02:34 AM

0 Likes
1
1238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-03 02:32 AM

Hello AmrMustafa,

 

To "if I connected all of panel to internet ( how much conflict between Group address for each panel )"

I guess that all floors have the same structure and does not need to communicate to each other from KNX-Point of view.
2022-02-03_10h26_15.png

If this is the case then you can select "TP-UART". If you are fully sure that you didnt want any KNX-IP-Features (use it as an interface) then you can untick the dedicated parameter.
can simply deactivate the KNX-Communication on IP-Side. Means each KNX-Communicationstays on the dedicated level/floor.

2022-02-03_11h09_01.png

If this is set you can still have the W4K connected to the internet to get for example the actual time which is needed for sunrise/sunset features.


To "I ask if I want to  control all panels from 1 workstation  how that ?"

You can create, just as one example, in the first W4K a custom visualization where you can integrate all 34 views of the TouchVisu. For that you need to create the dedicated structure to navigate between the different floors.
Each W4K (of each floor) needs to be included in a dedicated "Frame". Here you enter the dedicated URL of the TouchVisu of each W4K within the building.

 

 

Here you find the link to the dedicated manual to review all instructions more in detail.
https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=Wiser+for+KNX+%28LS... 

 

 

Kind regards
Thomas

Application Design Engineer
Tags (1)
  • Tags:
  • english
Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2022-02-03 02:36 AM

0 Likes
0
1236
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-03 02:36 AM

This picture belongs to the threat above within the section with the "Frame".
For some reasons I couldnt add it there.

2022-02-03_11h25_31.png

 


sorry for that

 

Kind regards
Thomas

Application Design Engineer
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore