Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

HomeLYnk - Maximum Modbus connections

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • HomeLYnk - Maximum Modbus connections
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Related Products
product field
SpaceLogic KNX - 4ʺ Touch Unit
product field
KNX Push Button Dynamic Labeling, universal
product field
Wiser for KNX : logic controller

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Start a Topic
Solved
DK-Michael
Commander DK-Michael Commander
Commander

Posted: ‎2016-03-07 12:37 AM . Last Modified: ‎2024-07-14 11:56 PM

0 Likes
2
1166
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-03-07 12:37 AM

HomeLYnk - Maximum Modbus connections

Hi

I have a customer who is going to install 158 iEM meters and needs a master unit where he can read the kWh values. I have suggested 1 x HomeLYnk with 5 x Link150 gateways to do it.

My question is regarding the maximum TCP connections for the Modbus TCP. The manual states that it is 100 x TCP connections but will the HomeLYnk create a TCP connection for each gateway or for each iEM meter? Cause if it is per iEM meter, he will need 2 x HomeLYnk and then exchange data between the two.

Please advise

Best regards, Michael

________________________________
Michael Johansen
Solution Architect
M +4528991535
E michael.johansen@se.com
LinkedIn https://www.linkedin.com/in/mich4el/
  • Thumbnail of SpaceLogic KNX - 4ʺ Touch Unit
    SpaceLogic KNX - 4ʺ Touch Unit
  • Thumbnail of KNX Push Button Dynamic Labeling, universal
    KNX Push Button Dynamic Labeling, universal
  • Thumbnail of Wiser for KNX : logic controller
    Wiser for KNX : logic controller
View products (3)
Tags (9)
  • Tags:
  • energy server
  • gateway
  • gateways
  • homelynk
  • modbus rs-485 rtu
  • modbus tcp
  • modbus_rtu
  • modbus_tcp
  • spacelynk
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
PetrMares
Commander PetrMares Commander
Commander

Posted: ‎2016-03-10 02:24 AM

3 Likes
1
1049
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-03-10 02:24 AM

Hello Michael,

If you have 158 iEM meters you need at minimum 2 homeLYnks (100 TCP connection is the limit). For this architecture You have to use spaceLYnks. homeLYnk is focused for residential and the price is not too different. What is more homeLYnk is limited to 10 Modbus device.

To IP input set IP address of Modbus IP gateway (Link150) and to Device address set slave address of power meter behind the Modbus gateway.

see picture:

ScreenShot651.jpg

I tested as a gateways EGX100, EGX300 and Smartlink IP, not Link150. The procedure should be the same.

Be careful only about CPU load. Pooling too many registers from too many devices in a minimum time cause higher CPU load. I've tested 10 power meters (each 10 registers, pooling time 60s) and the CPU load was 0.2 - 0.4 which is ok.

As you need to read one register from power meter it is ok from my point of view. Moreover what you want to read is Active energy and this is not necessary to read this value too often.

There is a lot of space for tuning anyway.

BR

Petr

See Answer In Context

Reply
Replies 2
PetrMares
Commander PetrMares Commander
Commander

Posted: ‎2016-03-10 02:24 AM

3 Likes
1
1050
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-03-10 02:24 AM

Hello Michael,

If you have 158 iEM meters you need at minimum 2 homeLYnks (100 TCP connection is the limit). For this architecture You have to use spaceLYnks. homeLYnk is focused for residential and the price is not too different. What is more homeLYnk is limited to 10 Modbus device.

To IP input set IP address of Modbus IP gateway (Link150) and to Device address set slave address of power meter behind the Modbus gateway.

see picture:

ScreenShot651.jpg

I tested as a gateways EGX100, EGX300 and Smartlink IP, not Link150. The procedure should be the same.

Be careful only about CPU load. Pooling too many registers from too many devices in a minimum time cause higher CPU load. I've tested 10 power meters (each 10 registers, pooling time 60s) and the CPU load was 0.2 - 0.4 which is ok.

As you need to read one register from power meter it is ok from my point of view. Moreover what you want to read is Active energy and this is not necessary to read this value too often.

There is a lot of space for tuning anyway.

BR

Petr

Reply
DK-Michael
Commander DK-Michael Commander
Commander

Posted: ‎2016-03-10 03:51 AM

0 Likes
0
1049
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-03-10 03:51 AM

Thanks Petr! I have sent your response to the customer.

________________________________
Michael Johansen
Solution Architect
M +4528991535
E michael.johansen@se.com
LinkedIn https://www.linkedin.com/in/mich4el/
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore