Dears
I'm trying to connect Modbus gateway from GREE ME50-00/EG(M) to control HVAC system via Wiser for KNX (LSS100100), but couldn't read the values, it always give me invalid CRC i tried to connect to AS-p and and everything worked normally,
the data as following :
baud rate: 9600bps; standard: RS485; Address = 2
What is the problem ?
thanks,
Link copied. Please paste this link to share this article on your social media post.
Hello Hamza_Nasri!
Would it be possible to share a tiny video of your connection and some pictures of your configuration/error message?
This would help to get a better understanding of your problem.
Link copied. Please paste this link to share this article on your social media post.
Dear @Thomas_Rohde ,
Kindly find attached data requested from your side,
Please let me know for any further clarifications,
Best Regards,
Link copied. Please paste this link to share this article on your social media post.
Hello Hamza_nasri!
Many THANKS for the material you shared. I would propose to enrich the profile with more attributes.
Beside that, I made some adaptations. Within the picture you can identify the differences:
I would propose to try the attached file (I had to zip it as the ending *.json is not accepted).
The changes will not help to find the device when you do a scan.
So you need to add it manually to the list of Modbus devices.
To make a quick test .. I would link a Group-Address to the "Ambient temperature"
in order to see if sensefull values coming.
You can also identify, that something is wrong, in case the Modbus-Device get highlighted in slight red color.
Please have also in mind that sometimes it is needed to shift the register-addresses by "1".
Please let me know 🙂
Link copied. Please paste this link to share this article on your social media post.
Device scan is not supported by all Modbus devices so this won’t tell you much.
Also starting with a template without testing the register(s) first (and see the correct value as a response) is not the best approach..
You should always start with the read test to determine the connection, registers and possibly if a -1 offset is needed.
With the results of your read test(s) you start building your profile or you end up facing the issues you have now..
Link copied. Please paste this link to share this article on your social media post.
Interesting fields in testing
The answer, validates comunication.. even if the answer is 0.