Hello,
Do we have full set of Modbus profile (.json) for sL and Wiser for KNX? Here is the modbus register table attached and the draft json file for single machine (1-00).
Please help to correct me if I'm wrong and I haven't any equipment to test at this moment.
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Hello,
Instead of focus on specific product we have created Application note Daikin HVAC Systems via CoolMasterNet
CoolMasterNet (CMN) is compatible with following HVAC manufacturers (attachment), but we tested with Daikin because they provided samples for verification
AN is available here: https://www.se.com/ww/en/download/document/AN041_SL/
Out of CMN we do not have json profile with complete registers for device you have.
Link copied. Please paste this link to share this article on your social media post.
Hello,
Instead of focus on specific product we have created Application note Daikin HVAC Systems via CoolMasterNet
CoolMasterNet (CMN) is compatible with following HVAC manufacturers (attachment), but we tested with Daikin because they provided samples for verification
AN is available here: https://www.se.com/ww/en/download/document/AN041_SL/
Out of CMN we do not have json profile with complete registers for device you have.
Link copied. Please paste this link to share this article on your social media post.
Hi Petr,
Thanks for reply. Yes, we have use Coolmaster before with success. However, the Daikin people already sold their official Modbus interface to customer and arrived already. Also I found that there are different model no. with more or less functions selling in Taiwan, China, Japan, Malaysia & some European countries.... and their protocol(Modbus register) are all nearly the same.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hi,
The change of the operation mode, fan speed, on/off need write a script to calculate final value by combining 3 objects together.
Unfortunately, I haven't finish the testing with Daikin on site.
onoff = grp.getvalue('1/1/1') -- fan on/off
direction = grp.getvalue('1/1/2') -- fan direction
speed = grp.getvalue('1/1/3') -- fan speed
value = bit.bor(
onoff and 1 or 0,
bit.lshift(bit.band(direction, 0x07), 8),
bit.lshift(bit.band(speed, 0x07), 12)
)
grp.update('1/1/4', value)
Link copied. Please paste this link to share this article on your social media post.
hello
i am having the same project using diakin Modbus interface to control the vrv units, please did you solve your problem? Do you have a correct diakin profile? Because i am having a problem reading from the registers ,the script always return nil
thanks for your support
Fadel