		Posted: 2016-12-06 10:56 PM . Last Modified: 2024-07-14 11:54 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
above attached file is regarding the mapping details of blue star vrv and I am integrated this with spacelynk through Modbus over rtu (rs 485) I have created the .json file for the same but it's not working. the .json that I created is attached below.
{
"manufacturer": "Blue Star",
"description": "Variable Refrigerant Volume",
"mapping": [
{ "name": "Actual Room Temperature", "bus_datatype": 7,"datatype":"int16",
"type": "inputregister", "address": 1, "value_multiplier": 0.1, "units": "°C" },
{ "name": "VRV on off", "bus_datatype": "int16", "type": "holdingregister","bus_datatype": 7,
"address": 1, "writable": true, "value_custom": {"0": "Off", "1": "On" } },
{ "name": "RUN MODE", "bus_datatype": "int16", "type": "holdingregister","bus_datatype": 7,
"address": 2, "writable": true, "value_custom": {"1": "Cool", "2": "Dry", "3": "Fan", "4": "Heat" } },
{ "name": "RUN FAN", "bus_datatype": "int16", "type": "holdingregister","bus_datatype": 7,
"address": 3, "writable": true, "value_custom": {"1": "Low", "2": "Medium", "3": "High", "4": "Auto" } },
{ "name": "SET TEMP", "bus_datatype": "int16", "type": "holdingregister","bus_datatype": 7,
"address": 4, "writable": true, "value_multiplier": 0.1, "units": "°C" }] , "manufacturer": "BLUESTAR",
"name": "VRV",
"product_range": "MODBUS CARD",
"description": "modbus - bluestar"
}
kindly support
 
					
				
		
Posted: 2016-12-14 10:42 PM
Link copied. Please paste this link to share this article on your social media post.
Hi Expert,
We did try with below scrip
[
{ "name": "Actual Room Temperature", "bus_datatype": 9, "datatype": "uint16", "type": "inputregister", "address": 0, "value_multiplier": 0.1, "units": "°C" }
{ "name": "VRV on off", "bus_datatype": 7, "datatype": "uint16","type": "register","address": 0, "writable": true, "value_custom": {"01": "Off", "10": "On" } },
{ "name": "Run Mode", "bus_datatype": 7, "datatype": "uint16", "type": "register", "address": 1, "writable": true, "value_custom": {"1": "Cool", "2": "Dry", "3": "Fan","4": "Heat", } },
{ "name": "RUN FAN", "bus_datatype": 7, "datatype": "unit16","type": "register","address": 2, "writable": true, "value_custom": {"1": "Low", "2": "Medium", "3": "High", "4": "Auto" } },
{ "name": "SET TEMP", "bus_datatype": 9, "datatype": "unit16","type": "register","address": 3, "writable": true, "value_multiplier": 0.1, "units": "°C" }] ,

We mange to get the value, but unable to change the value via SL would like to seek for expert help on it.
Link copied. Please paste this link to share this article on your social media post.
Hi Expert,
As of now Run mode command and on/off command is working however many times the commands bounce back. Let say when I give on command the value changes to on but after 3-4 seconds the value again changes to off.
bit value for on/off = 1:off ; 16:on
Also the blue star vrv is not taking the set point command . However on modscan it is working fine.
Link copied. Please paste this link to share this article on your social media post.
Hi Team,
Rest of the commands are working as of now, only temperature set point command(writable) is not working. Can anyone help me out for the same. I am using below mentioned code.
{"name": "SET TEMP", "bus_datatype": 9, "datatype": "unit16","type": "register","address": 3, "writable": true, "value_multiplier": 0.1, "units": "°C" }
 
					
				
				
			
		