SpaceLogic KNX Forum
Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.
Posted: 2016-11-17 06:51 PM . Last Modified: 2024-07-14 11:54 PM
Link copied. Please paste this link to share this article on your social media post.
Any one used spacelynk as a counter and timer for a signal channel?
I have a project has about 1000 channels, so if I need to count how many times each of them has been turned on and how long each of them has been turned one, how many spacelynks do i need? Is one enough?
Link copied. Please paste this link to share this article on your social media post.
Hello,
spaceLYnk can handle more than 3000 group address (1000 objects, 1000 timers, 1000 counters). Just keep in mind if channels rehresh (change period) is too fast, this might have some troubles with that.
Can you specify detailed how fast and whitch datatype are those channels?
Thank you.
David.
Posted: 2016-11-29 12:20 AM
Link copied. Please paste this link to share this article on your social media post.
all channels are switches, we just need to calculate ON/OFF times and run time. So, how many SL do we need for 1000 switch channels.
BTW, a third party willing to let us write their SDK, is that possible to achieve for SL?
Link copied. Please paste this link to share this article on your social media post.
Hello,
I think one can handle this, but for optimal performance I suggest you use two spaceLYnks.
I am sorry I don't understand your second question. What is SDK?
Thank you.
David
Link copied. Please paste this link to share this article on your social media post.
Hello,
Is this topic answered?
If yes, please mark it as answered.
Thank you
David
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.