DALI gateway turns on all the lights randomly

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • DALI gateway turns on all the lights randomly
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
121
Erwin-vd-Zwart
Sisko Erwin-vd-Zwart Sisko
54
Heribert_Dölger
Lt. Commander Heribert_Dölger Lt. Commander
30
FZetina
Lt. Commander FZetina Lt. Commander
27
View All
Related Products
product field
SpaceLogic KNX - 4ʺ Touch Unit
product field
KNX Push Button Dynamic Labeling, universal
product field
Wiser for KNX : logic controller

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Solved
joseloureiro
Crewman joseloureiro
Crewman

Posted: ‎2023-07-19 09:14 AM . Last Modified: ‎2024-07-14 11:42 PM

0 Likes
1
1632
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-07-19 09:14 AM

DALI gateway turns on all the lights randomly

Hi,

 

I'm currently working on a project with a couple dozen DALI Gateways (MTN6725-0004). Some of the gateways randomly turn on every light on both channels. At the moment I detected this issue in 3 gateways but there might be more.

 

I left a laptop on site recording the KNX network traffic overnight and searched for the moment any DALI gateway would send a status value telegraam of 100% on all their groups. I found out that there's no telegraam sent by any device that would trigger this behaviour.

 

This behaviour is exacly the same as to what would happen if the gateways were powered off because every group is configured with "Value on DALI Power Fail: 100%". But I don't think the gateways are losing power as they are all connected to the same UPS.

 

How can I troubleshoot this problem?

 

PS: Telegraam written wrong because somehow the word is not permitted in this community

  • Thumbnail of SpaceLogic KNX - 4ʺ Touch Unit
    SpaceLogic KNX - 4ʺ Touch Unit
  • Thumbnail of KNX Push Button Dynamic Labeling, universal
    KNX Push Button Dynamic Labeling, universal
  • Thumbnail of Wiser for KNX : logic controller
    Wiser for KNX : logic controller
View products (3)
Labels
  • Labels:
  • Protocols
  • Scripts
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Heribert_Dölger
Lt. Commander Heribert_Dölger Lt. Commander
Lt. Commander

Posted: ‎2023-07-20 04:44 AM . Last Modified: ‎2023-07-20 04:46 AM

0 Likes
0
1626
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-07-20 04:44 AM

Hello Joseloureiro

 

Difficult to say why this is happening.

 

I assume that the ECGs indeed go to DALI power failure mode.

 

A DALI power failure could happen due to
- loose contact in the DALI wiring
- defective ECG
- DALI line is overloaded (the gateway will switch off the DALI power when there is more than 250mA current on the line (but normally should not happen as an ECG is only allowed to have a consumption of 2mA))

 

All the above mentioned possible reasons are related to the dedicated DALI line. As you are using 2-channel DALI gateway it is not very likely that the same incident occurs on both DALI lines at the same time. But maybe you should double check if it really happens on both DALI lines at the same time.

 

Another possible reason might be that when switching from mains power to UPS there is a short delay until the UPS power is available and the gateway then is not powered for a few seconds. This could be enough that the gateway stops providing DALI power and due to that the ECGs go to 100%.

 

Another point to check is settings of the behaviour at KNX power failure and recovery (in case the KNX power supply is not buffered by UPS). In case of KNX power failure and recovery the gateway might send values to the ECGs depending on the settings in ETS. Best setting might be to select "set to last value".

 

To come closer to the root cause you might monitor the communication on the DALI line. For that you would need DALI monitor software (like Tridonic masterCONFIGURATOR which is free of charge) and a DALI interface to connect the PC to the DALI line. If no command is sent by the gateway in failure case then it is clearly a behaviour executed by the ECG itself. If there is commands coming from the gateway we need to check why the gateway is sending such commands.

 

You might also make different failure settings for line 1 and line 2 in one gateway and check if the result is same or different. Or you configure two gateways with different settings on power failure and see if there is a difference or not.

See Answer In Context

Reply
Reply 1
Heribert_Dölger
Lt. Commander Heribert_Dölger Lt. Commander
Lt. Commander

Posted: ‎2023-07-20 04:44 AM . Last Modified: ‎2023-07-20 04:46 AM

0 Likes
0
1627
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-07-20 04:44 AM

Hello Joseloureiro

 

Difficult to say why this is happening.

 

I assume that the ECGs indeed go to DALI power failure mode.

 

A DALI power failure could happen due to
- loose contact in the DALI wiring
- defective ECG
- DALI line is overloaded (the gateway will switch off the DALI power when there is more than 250mA current on the line (but normally should not happen as an ECG is only allowed to have a consumption of 2mA))

 

All the above mentioned possible reasons are related to the dedicated DALI line. As you are using 2-channel DALI gateway it is not very likely that the same incident occurs on both DALI lines at the same time. But maybe you should double check if it really happens on both DALI lines at the same time.

 

Another possible reason might be that when switching from mains power to UPS there is a short delay until the UPS power is available and the gateway then is not powered for a few seconds. This could be enough that the gateway stops providing DALI power and due to that the ECGs go to 100%.

 

Another point to check is settings of the behaviour at KNX power failure and recovery (in case the KNX power supply is not buffered by UPS). In case of KNX power failure and recovery the gateway might send values to the ECGs depending on the settings in ETS. Best setting might be to select "set to last value".

 

To come closer to the root cause you might monitor the communication on the DALI line. For that you would need DALI monitor software (like Tridonic masterCONFIGURATOR which is free of charge) and a DALI interface to connect the PC to the DALI line. If no command is sent by the gateway in failure case then it is clearly a behaviour executed by the ECG itself. If there is commands coming from the gateway we need to check why the gateway is sending such commands.

 

You might also make different failure settings for line 1 and line 2 in one gateway and check if the result is same or different. Or you configure two gateways with different settings on power failure and see if there is a difference or not.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of