Hello
how to Show/control each ECGs Group Object, I see only Groups from 1-16, but how to show the Group Objet for each ECG for MTN6725-0003?
- Labels:
-
Documents
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi @IC_Systems,
to be honest ... I am not sure that I got your question correctly.
Currently our DALI-Basic-Gateway can only handle up to 16 DALI-Groups and NO single ECGs.
In case you want to control a single ECG with a DALI-GW-Basic you need to put just one ECG in one DALI-Group or you switch to our DALI-GW-Pro (MTN6725-0101 ).
Thomas
Application Design Engineer
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi @IC_Systems,
to be honest ... I am not sure that I got your question correctly.
Currently our DALI-Basic-Gateway can only handle up to 16 DALI-Groups and NO single ECGs.
In case you want to control a single ECG with a DALI-GW-Basic you need to put just one ECG in one DALI-Group or you switch to our DALI-GW-Pro (MTN6725-0101 ).
Thomas
Application Design Engineer
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Thak you @Thomas_Rohde
So in DALI-GW Basic, I can't control each ECG separately from 1-64, only groups of control are allowed 1-16. Right?
But I can control a single ECG using MTN6725-0101 or MTN6725-0001.