Cyrillic characters are displayed incorrectly on MTN6215-5910

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • Re: Cyrillic characters are displayed incorrectly on MTN6215-5910
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
121
Erwin-vd-Zwart
Sisko Erwin-vd-Zwart Sisko
54
Heribert_Dölger
Lt. Commander Heribert_Dölger Lt. Commander
30
FZetina
Lt. Commander FZetina Lt. Commander
27
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Solved
Yevhenii_Kuz
Ensign Yevhenii_Kuz Ensign
Ensign

Posted: ‎2024-09-25 03:58 AM

0 Likes
5
634
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-25 03:58 AM

Cyrillic characters are displayed incorrectly on MTN6215-5910

When trying to give the screen name in cyrillic characters in ETS6, we get an incorrect display on the MTN6215-5910 character set:

Yevhenii_Kuz_0-1727261173376.pngYevhenii_Kuz_1-1727261538781.jpeg

 

 

  • Thumbnail of SpaceLogic KNX - 4ʺ Touch Unit
    SpaceLogic KNX - 4ʺ Touch Unit
View products (1)
Labels
  • Labels:
  • SpaceLYnk
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Heribert_Dölger
Lt. Commander Heribert_Dölger Lt. Commander
Lt. Commander

Posted: ‎2024-09-30 07:22 AM

1 Like
1
522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-30 07:22 AM

Hello

 

The root cause most probably is wrong setting of codepage in ETS project settings. You have to select Cyrillic as codepage in your ETS project settings. See attached picture of ETS5. After the change of the setting to Cyrillic you need to download application once again to Multitouch Pro. 

 

I tested it and worked well on my side, see attached picture. 

See Answer In Context

Attachments
Reply
Replies 5
Heribert_Dölger
Lt. Commander Heribert_Dölger Lt. Commander
Lt. Commander

Posted: ‎2024-09-27 05:52 AM . Last Modified: ‎2024-09-27 05:54 AM

1 Like
1
578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-27 05:52 AM

Hello

 

Could you please let me know which firmware version you are using? Version is indicated on the starting screen directly after powering the device (named as "server"version).

 

Cyrillic characters are only supported since firmware version 30.7. If you have lower version you need to upgrade firmware.

 

MT Pro with firmware 30.7, when powered for the first time start with a selection screen for character set. You can choose between Europe, Cyrillic, Hebrew and Greek and confirm with a long press (>10sec) on the OK button. This selection sreen will appear only one time. To properly show Cyrillic characters you need to select the Cyrillic character set. 

 

If you made the wrong selection and want to change it later you need to configure a screen in ETS showing the settings menu and download this configuration to the MT Pro. After that you can access the selection screen and change the setting.

 

Best regards
Heribert

Reply
Yevhenii_Kuz
Ensign Yevhenii_Kuz Ensign
Ensign

Posted: ‎2024-09-30 01:21 AM

0 Likes
0
537
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-30 01:21 AM

Hello! Thank you for your reply!

I'm using version 30.7. The result that you can see in the second image is displayed in Cyrillic letters (as configured), but not correctly! It should be “Екран 1” but it displays “Хъ№рэ 1”.

 

 



 

 

Reply
Heribert_Dölger
Lt. Commander Heribert_Dölger Lt. Commander
Lt. Commander

Posted: ‎2024-09-30 07:22 AM

1 Like
1
523
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-30 07:22 AM

Hello

 

The root cause most probably is wrong setting of codepage in ETS project settings. You have to select Cyrillic as codepage in your ETS project settings. See attached picture of ETS5. After the change of the setting to Cyrillic you need to download application once again to Multitouch Pro. 

 

I tested it and worked well on my side, see attached picture. 

Attachments
Reply
Yevhenii_Kuz
Ensign Yevhenii_Kuz Ensign
Ensign

Posted: ‎2024-09-30 07:56 AM

1 Like
0
513
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-30 07:56 AM

Hello

 

Thank you very much! It worked. 

Reply
Heribert_Dölger
Lt. Commander Heribert_Dölger Lt. Commander
Lt. Commander

Posted: ‎2024-09-30 08:01 AM

1 Like
0
511
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-30 08:01 AM

Happy to hear that your problem is solved. 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of