Will the 5500 SHAC/NAC get native integration with HomeKit?

SpaceLogic C-Bus Forum

Schneider Electric forum about the C-Bus platform to get support and share knowledge including Network Automation Controller (NAC), Application Controller (AC) at selection, installation and troubleshooting sides.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic C-Bus Forum
  • Will the 5500 SHAC/NAC get native integration with HomeKit?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sesa96364
sesa96364 Schneider Alumni (Retired)
9
KCWong
Lieutenant KCWong Lieutenant
4
ZeeZee97
Administrator ZeeZee97 Administrator
1
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to SpaceLogic C-Bus Forum
Start a Topic
psionic001
psionic001
Cadet

Posted: ‎2024-11-23 05:39 PM

0 Likes
10
2234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-23 05:39 PM

Will the 5500 SHAC/NAC get native integration with HomeKit?

Hi @Asli,

 

When will the 5500SHAC gain integration with HomeKit and other smart devices?

 

Schneider made an announcement some time ago about Matter integration:

https://www.se.com/ww/en/about-us/newsroom/news/press-releases/schneider-electric-to-integrate-new-%...

 

Thanks

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 10
Digby_Brock
Ensign Digby_Brock
Ensign

Posted: ‎2025-01-07 12:08 AM

1 Like
0
2151
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-07 12:08 AM

Hi,

I've been playing around with the existing app for the KNX devices and made a few modifications to enable control with the c-bus data types. I've posted this on the c-bus forums website if you want to take a look. Note this is not official, so theres a lot not supported, just brightness, window coverings and switch at this stage, but it does work quite well.

Link to c-bus forums thread here: https://www.cbusforums.com/threads/5500ac2-nac2-firmware-v2-0-0-homekit-app.11357/ 

Reply
Mr_C
Ensign Mr_C Ensign
Ensign

Posted: ‎2025-01-13 11:43 PM

1 Like
2
2130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-13 11:43 PM

Hi 

The 5500AC2 and 5500NAC2  will in future have a migration of the Homekit Application ported specifically for working with the C-Bus System   

This will make its way to version 2.0 firmware for these devices,  

 

But it will not be made available to the  5500SHAC,  LSS5500SHAC, 5500NAC and LSS5500NAC  firmware.  

An ETA for this Application is not being provided at this time,  it is a Baclog item alogn with many other applications.  

Currently the focus is on delivering,  The Application Framework as a whole,  Cloud Connectivity to the Controller,  and Mobile Applications Supported by Manager,  

We May look to incorporate HomeKit with other functions in Manager Application,  such as the Voice Enablement for Alex and Google Home,   but we will wait and see.   

Now is however a good time for you to provide your input to what if anything you like to see done with C-Bus and HomeKit that might be different to what has been done by Logic Machine.  



Schneider Electric Australia PTY
Reply
Digby_Brock
Ensign Digby_Brock
Ensign

Posted: ‎2025-01-14 03:24 AM

0 Likes
1
2114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-14 03:24 AM

The Attached is a quick crude mock up of something i had in mind after using the app for a while and finding it quite repetative. The following could be a faster user friendly way to implement the mapping.

On app Initialisation automatically add all the Controllers existing objects / Tags to a list and provide a refresh button to check for any new or removed tags there after. 

As C-bus only requires the one address unlike KNX which uses multiple address's for 1 bit, 1 byte and status ect, we can simplify the mapping.

list all the existing tags with a checkbox for each disabled by default so the user can choose what to pass to homekit, display the group address for information purposes, take the existing tag name by default ( can be manually edited when edit button pressed ), Type can be a dropdown list, default type to be brightness ( assuming most groups will be lighting, can be manually edited when edit button pressed ), display the corrosponding homekit Characteristic for information, provide an edit button when pressed, name can be manually edited and type can be changed by dropdown list, click edit again to save changes and lock fields. If enable is checked the mapping is added / refreshed to homekit database and controllable, if not it's hidden from homekit.  

Untitled.png

 




 

Attachments
Reply
Mr_C
Ensign Mr_C Ensign
Ensign

Posted: ‎2025-01-14 09:57 PM

0 Likes
0
2088
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-14 09:57 PM

Thanks for that Input 

I will take that on advice but also potentially mix it up with where we are going in the new firmware to make the process even simpler or faster.  

The current benefit we have with C-Bus as you point out is that there is One object only for the control of any load type,  this object contains the Control and State or current value  of the item as well.   This Simplifies things as we do not need to create a relation ship between objects. 

In addition we have added in new firmware, a function definition to the General Control Applications (control applications are what you refer to as Lighting Application) so that's any Object assigned to a Application in the address range of 42 - 127 the most common one being there by default is 56 which we title lighting.   This feature automatically then defines what is the function of the object,  such as Lighting On/Off  vs Lighting with Dimming,  or  if the Object is Fan Control  Blind Control etc.  

It will still be a little time before these functions are being defined by the project you transfer over from the commission software,  but as that falls into place we can automate the Characteristics process as well.  

Again I also see that we may make this part of the Manager Application along with other Voice control platforms,  as previously mentioned. 

To me this makes sense as Manager application,  basically defines what will be present on the customers Mobile devices,   both in our own dedicated Mobile apps,  but why not in homekit as well.   

Be interested to hear your thoughts,   but also understand that currently you may not have a great deal of experience with the Manager Application, or mobile apps,  but it is coming.  

Schneider Electric Australia PTY
Reply
Digby_Brock
Ensign Digby_Brock
Ensign

Posted: ‎2025-01-14 10:59 PM

0 Likes
0
2068
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-14 10:59 PM

I've played with the manager app a little, but no a geat deal to be honest, would be nice to see how it looks on a mobile but i havent seen the moblie app in the app store yet. Going by the PDF guide it looks quite nice on the mobile, would it be possible to have a similar look in the web view opposed to the large widget tiles?

Reply
Digby_Brock
Ensign Digby_Brock
Ensign

Posted: ‎2025-01-15 12:23 AM

0 Likes
0
2058
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-15 12:23 AM

As for creating the control elements on the manager app, i feel the same aproach with a list view would be handy, list all the objects similar to the suggest homekit layout described above, add extra column to select floor and room via dropdown, default the widget type to the c-bus application types as you have mentioned, or manually select an alternative via dropdown. Title name default is taken from the tag.

 

May be a bit trickier for the multi button widgets but certantly a lot quicker for the single element ones opposed to clicking the + icon, scrolling to select the widget, manually typing a title then saving for each one.

 

Event if its just a seperate page in the manager called "Bulk configure". after which the installer can manually adjust the widgets using the existing edit icon.

 

Personally id like the homekit app to remain indepandant, there may be instances where he manager app is not required, or instances where homekit is not required, and it may be more effective and timely to deliver seperate apps as opposed to waiting for the release of 1 app to rule them all.

Reply
ozbridge
ozbridge
Cadet

Posted: ‎2025-01-17 11:52 AM

0 Likes
1
1953
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-17 11:52 AM

Thank you for the update. Can you please explain why the 5500NAC will not get the update? The devices are almost identical - surely this isn’t a hardware limitation? 

it would be good to see at least the 5500NAC which was designed for larger applications get the 2.0 firmware features the 2.0 devices are getting.

Thank you for your consideration.

Reply
Mr_C
Ensign Mr_C Ensign
Ensign

Posted: ‎2025-01-27 09:22 PM

0 Likes
0
1884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-27 09:22 PM

So 5500NAC and 5500SHAC, do get Firmware 2.0 but this build of firmware for these devices is primarily security fixes,  and additional features that are added to the existing configurator / visualizations + C-Bus Application support. 
 
There are some significant Hardware/Platform differences between V1 5500NAC  and V2 5500NAC2,  The environment is not being developed for 5500NAC/SHAC to support Application modules. 

Schneider Electric Australia PTY
Reply
Digby_Brock
Ensign Digby_Brock
Ensign

Posted: ‎2025-08-05 04:27 AM . Last Modified: ‎2025-08-06 01:18 AM

1 Like
0
1031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-05 04:27 AM

Small update for anyone who wanted to try this, finally added a Mass Add Button as described above earlier:

https://www.cbusforums.com/threads/5500ac2-nac2-firmware-v2-0-0-homekit-app.11357/#post-62281

Reply
Digby_Brock
Ensign Digby_Brock
Ensign

Posted: ‎2025-11-23 12:27 PM

0 Likes
0
274
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-23 12:27 PM

Updated version with Float16 conversion for Temperature

https://www.cbusforums.com/threads/5500ac2-nac2-firmware-v2-0-0-homekit-app.11357/page-2


Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore