Schneider Electric forum about the C-Bus platform to get support and share knowledge including Network Automation Controller (NAC), Application Controller (AC) at selection, installation and troubleshooting sides.
Posted: 2025-06-24 03:32 PM . Last Modified: 2025-06-24 03:36 PM
Updated NAC2 as usually performed.
Was on firmware 2.1.0 prior to the update.
Connected via hardwired Ethernet connection.
Using Edge.
Added 2.2.0 img and sig file
Update performed fine, NAC rebooted.
After reboot was unable to get into the configuration via the web interface.
Entered password and each time page would reload.
Cleared cache, tried another browser all failed.
Interesting that I could log into the app store fine using the same password.
Factory reset device by holding the SR for 30 sec.
IP address confirmed changed after reset.
Connected via USB entered default password and still not able to login.
Tried reset multiple time same result.
Now have a bricked NAC. Any idea's?
Hi Mark
I believe this issue has been addressed with your REP, the unit has been replaced and firmware update on new unit worked fine, The Failed unit will be returned for investigation of the issue.
Hi Mark,
Thanks for the detail, investigation underway through case management channel.
Has 2.2.0 been pulled? it doesn't appear in the downloads section.
There has been some isolated issues associated with the upgrade to Firmware V2.2.0 which prevents successful login to the Controller.
The Firmware has since been removed for download and a fix has been identified which will be available in the next Firmware release.
If you have experienced this issue, please contact Customer Care to resolve the issue.
If you have already downloaded Version 2.2.0 firmware, please delete this file and refrain from updating any additional controllers with this firmware. However, if you have already updated a controller and it is functioning properly, no further action is needed until a future firmware version is released.