soft starter for asynchronous motor

Solutions for Motor Management

Get support to configure, troubleshoot, update or upgrade your motor management solution built with Altivar variable speed drives and Tesys devices to start, control, protect and monitor Low Voltage and Medium Voltage motors and loads, covering direct start, soft start and variable speed control.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Solutions for Motor Management
  • soft starter for asynchronous motor
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BJacqz
Commander BJacqz Commander
48
LeoLazzaro
Lieutenant LeoLazzaro Lieutenant
16
PriscilaCunha22
Lieutenant JG PriscilaCunha22 Lieutenant JG
12
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
9
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Solutions for Motor Management
Mick1234
Crewman Mick1234
Crewman

Posted: ‎2025-02-11 12:35 PM

0 Likes
4
272
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-11 12:35 PM

soft starter for asynchronous motor

I’ve got a fan with a very heavy blade and it takes about 10 second to get up to speed. The problem is, by that time the overload sometimes trips or the fuse blows on the supply transformer.

 

What I need is to reduce the starting current and allow the fan to accelerate more gradually.

The motor is 110V single phase, with a running current of 16A and a peak DOL start current of around 80A.

 

I thought the “ATS01N125FT, 110V - 480V Soft Starter for Asynchronous Motors” would be perfect for the job, but it didn’t have the expected results. Even with the start time set to maximum, there didn’t seem to be any difference in start up time or start up current and the fuses still kept blowing and overload tripping. I tried various initial voltages, but it didn’t seem to make much difference.

 

How do I extend the start up time beyond 10 seconds, or is that the limit for this device?

 

The unit is wired as shown on the drawings that came with the unit for single phase motors. I’m I doing something wrong?

  • Tags:
  • ATS01N125FT
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Mick1234
Crewman Mick1234
Crewman

Posted: ‎2025-02-24 04:16 AM

0 Likes
0
201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-24 04:16 AM

After another site visit with more detail monitoring, I found with the ATS01N125FT set to maximum time, that it hit full voltage after 6 seconds and in 3 seconds when set to the minimum time.

 

I need much longer starting times. Do I have a faulty unit or is 6 seconds the maximum start time?

Reply

Link copied. Please paste this link to share this article on your social media post.

NeiB
Lieutenant NeiB Lieutenant
Lieutenant

Posted: ‎2025-02-25 03:30 AM . Last Modified: ‎2025-02-25 03:32 AM

0 Likes
1
196
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-25 03:30 AM . Last Modified: ‎2025-02-25 03:32 AM

Dear @Mick1234 ,

 

Hope you are doing well.

 

Yes, the maximum starting time of ATS01 ending in FT is 5 seconds as indicated on the documentation attached (the table below):

 

NeiB_0-1740482212046.png

 

Sadly this is the only model on the Altistart family dedicated to single phase application. The models for three phase does have a longer starting time and a BOOST function to improve start torque however it does not work with single phase systems.

 

Best Regards,

 

Neide

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Mick1234
Crewman Mick1234
Crewman

Posted: ‎2025-02-27 11:56 AM

In response to NeiB
0 Likes
0
180
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-27 11:56 AM

Well, that was a waste of £££ then! 🙄

Thank you for sharing the information. The PDF I downloaded didn’t have that detail.

 

I assumed there would be a sufficient start up time. I mean, why would anyone make a soft starter with a shorter start time then when the motor starts up direct on line! The whole purpose of a soft start is to extend the start time.

Reply

Link copied. Please paste this link to share this article on your social media post.

NeiB
Lieutenant NeiB Lieutenant
Lieutenant

Posted: ‎2025-02-28 03:45 AM

0 Likes
0
171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-28 03:45 AM

Hi @Mick1234 ,

 

Yes, sorry to hear that.

 

The point is that ATS01 has been in the market for a while and it used to be suitable for most of the standard application, however this has changed a lot lately.

 

I recommend that every time you have an application with our products that are new to you, come to our community and ask to see if more knowledge is available to help you to take a better decision and not waste $$$ again.

 

There is also the technical support of Schneider in your country that is available for whatever question you have.

 

See you.

 

Best Regards,

 

Neide

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of