Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Soft starter

Solutions for Motor Management

Get support to configure, troubleshoot, update or upgrade your motor management solution built with Altivar variable speed drives and Tesys devices to start, control, protect and monitor Low Voltage and Medium Voltage motors and loads, covering direct start, soft start and variable speed control.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Solutions for Motor Management
  • Soft starter
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BJacqz
Commander BJacqz Commander
49
LeoLazzaro
Lieutenant LeoLazzaro Lieutenant
16
PriscilaCunha22
Lieutenant JG PriscilaCunha22 Lieutenant JG
15
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Solutions for Motor Management
Start a Topic
Shinekhuu
Shinekhuu
Cadet

Posted: ‎2025-01-10 05:46 PM

0 Likes
3
919
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-10 05:46 PM

Soft starter

I want to size a soft starter to following freezer. 

 

Single phase, 660W, 110V

Starting current 45A

 

I was wondering if I can use 25A single phase ATS01 starter.

Soft starter:https://www.se.com/jp/ja/product/ATS01N125FT/ats01-%E3%82%BD%E3%83%95%E3%83%88%E3%82%B9%E3%82%BF%E3%...

 

Main source is single phase 110V and 30A. Please help.

 

 

 

 

 

Labels
  • Labels:
  • Connectivity
  • Material Handling
  • Safety
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2025-01-13 09:55 PM

1 Like
0
900
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-13 09:55 PM

Hi,

The choosen soft starter is a 3 phase model. So far I understand you has an 1 phase freezer. In that case I would suggest to use a 1 phase model like ATS01N106FT. 

The starting current of the compressor is in my opinion not the correct value to select the soft starter. Because this one should be reduced through the soft starter.  

Alternative you could also the next bigger one to have more safety.

But in any case im not 100% sure that the compressor of the freeezer will start in any case. Normally the compressors in freezers in 1 phase with capacitor are weak from the starting torque. The use of the softstarter will reduce the torque. This could be a problem, but it could also work. It is hard to say from distance.

Bastian_Schmitz_0-1736833789942.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

otrotabi
Commander otrotabi
Commander

Posted: ‎2025-01-15 03:44 AM

0 Likes
0
859
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-15 03:44 AM

One way to minimize the needed torque is to equalize low pressure side with high pressure side (on the refrigeration circuit itself). If it is a standard commercial freezer there´s usually a capillary tube before the evaporator and all you need to do is to allow enough time  and it will equalize by itself. But if there´s a TXV valve (or a liquid solenoid valve which would be rare on a small freezer) you would probably need to make sure the circuit is not unbalanced when trying to start it. Some people use a bypass solenoid for the TXV which is off once the compressor starts.

 

The kind of compressors used in refrigeration for small freezers generally have an internal bi-metal overload which means that if the motor does not start the circuit opens thus protecting the motor. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BrownSugar
Lieutenant JG BrownSugar Lieutenant JG
Lieutenant JG

Posted: ‎2025-09-18 05:33 AM . Last Modified: ‎2025-09-18 05:34 AM

0 Likes
0
362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-18 05:33 AM . Last Modified: ‎2025-09-18 05:34 AM

Thank you for your request. I believe the ATS01N125FT is not suitable for this application. The freezer motor is 660 W, 110 V, single-phase, with a running current of about 6 A but a starting current of 45 A. The ATS01N125FT is rated for 25 A nominal, and that rating applies to steady-state current. It cannot handle a 45 A inrush without tripping or overheating. In addition, the ATS01 is a voltage ramp soft starter with a short ramp time of 1–5 seconds and no true current limit. For a heavy start, the current will still spike close to direct-on-line levels. 
The recommended solution is to replace the single-phase motor with a three-phase motor and use an Altivar drive. This allows a long acceleration time of 20–30 seconds or more and provides current limit to protect fuses and the transformer.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore