SLF1 error on stopping modbus connection

Solutions for Motor Management

Get support to configure, troubleshoot, update or upgrade your motor management solution built with Altivar variable speed drives and Tesys devices to start, control, protect and monitor Low Voltage and Medium Voltage motors and loads, covering direct start, soft start and variable speed control.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Solutions for Motor Management
  • SLF1 error on stopping modbus connection
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BJacqz
Commander BJacqz Commander
48
LeoLazzaro
Lieutenant LeoLazzaro Lieutenant
16
PriscilaCunha22
Lieutenant JG PriscilaCunha22 Lieutenant JG
12
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
9
View All
Related Products
product field
Schneider Electric
Low Voltage AC Building Drives

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Solutions for Motor Management
YorickBM
Crewman YorickBM
Crewman

Posted: ‎2023-02-06 01:35 AM . Last Modified: ‎2023-02-17 06:44 AM

0 Likes
3
4361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-02-06 01:35 AM . Last Modified: ‎2023-02-17 06:44 AM

SLF1 error on stopping modbus connection

Hi All,

 

Currently, I'm working on a python program that uses serial Modbus to communicate with an ATV320 drive. 

Once my program finishes and the keep-alive ping of every second stops, when the Modbus timeout amount is reached in the ATV320 it will go into SLF1 fault. What do I need todo so it does not go into SLF1 fault? Currently, my program runs the following Modbus sequence:

 

8501 -> 0x0006 

8501 -> 0x0007

(Startup done)

 

8502 -> 500 (Set frequency reference of ATV320)

8501 -> 0x040F (Start conveyer belt in reverse altho reverse isn't working?? just keeps going forward)

(Run for a period of time)

 

8501 -> 0x0007

8501 -> 0x0006

8501 -> 0x0000

8502 -> 0x0000

(keep-alive also stops now, after set Modbus timeout SLF1 error pops up)

Labels
  • Labels:
  • Low Voltage AC Drives
  • Tags:
  • atv320
  • english
  • modbus
  • RS458
  • Serial Modbus
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
LeoLazzaro
Lieutenant LeoLazzaro Lieutenant
Lieutenant

Posted: ‎2023-03-13 08:36 AM

0 Likes
0
4299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-13 08:36 AM

Hi YorickBM

Sorry I'm not familiar with python program, but PLCs are always writting the CMD (8501) and RFR (8502). The drive recognozes a fault SLF1 when It has not received any package during Time out , then when time out is reached , the drive trigger SLF1. Please try to write this 2 parameters before the time out to keep alive the comunication .For other hand , reverse is 080F hex. Please refer to the Modbus communication manual

https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=ATV320_Modbus_manua...

Thank you in advance

B.R.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Ahmed_Alzafer
Lieutenant JG Ahmed_Alzafer Lieutenant JG
Lieutenant JG

Posted: ‎2023-03-14 01:41 AM

0 Likes
1
4295
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-14 01:41 AM

Hello,

 

In fact this is a normal behavior. At first time you write the frequency by Modbus, the drive will begin to monitor Modbus channel, to check that the controller write or read at least one time during the time set in parameter TTO.

Assuming that TTO is set to 30s, then when you write Frequency by modbus, you will have 30s at most to send any read or write request by the controller to the drive before SLF1 fault appears.

 

This is described on ATV320 Modbus manual:

 

Capture.JPG

Reply

Link copied. Please paste this link to share this article on your social media post.

YorickBM
Crewman YorickBM
Crewman

Posted: ‎2023-03-14 01:57 AM

In response to Ahmed_Alzafer
0 Likes
0
4292
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-14 01:57 AM

Hey, I know what causes this error to occur since I have read the manuals provided.

For my case it was a question of is there a way to PREVENT this error from occuring if the disconnection is deliberately done. As described in the post I send the commands to turn off the ATV320 (as described in their manual).

Now it basically forces you to use fault reset every time I would reconnect with my program..... How can I prevent the SLF1 error when disconnecting deliberately with the ATV320 after shutdown commands are send described in the manuals.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of