Ask our Experts
Didn't find what you are looking for? Ask our experts!
Get support to configure, troubleshoot, update or upgrade your motor management solution built with Altivar variable speed drives and Tesys devices to start, control, protect and monitor Low Voltage and Medium Voltage motors and loads, covering direct start, soft start and variable speed control.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-25 01:54 PM
Hi,
Is it possible to daisy chain multiple ATV320 on Modbus RTU using embedded RJ45 connection?
If so, what is best practice?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-28 01:39 PM
Yes it is possible, the best solution is to use the VW3A8306TF03 "T" branch and the VW3A8306RC termination resistor
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-28 01:39 PM
Yes it is possible, the best solution is to use the VW3A8306TF03 "T" branch and the VW3A8306RC termination resistor
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.