Hi,
Is it possible to daisy chain multiple ATV320 on Modbus RTU using embedded RJ45 connection?
If so, what is best practice?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-28 01:39 PM
Yes it is possible, the best solution is to use the VW3A8306TF03 "T" branch and the VW3A8306RC termination resistor
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-28 01:39 PM
Yes it is possible, the best solution is to use the VW3A8306TF03 "T" branch and the VW3A8306RC termination resistor