How to assign a bit 12 to 15 in control word ATV 630 drives using CiA 402 profile
  • Industrial Automation
  • Solutions for Motor Management
  • How to assign a bit 12 to 15 in control word ATV 630 drives using CiA 402 profile
BJacqz
Commander BJacqz Commander
49
LeoLazzaro
Lieutenant LeoLazzaro Lieutenant
16
PriscilaCunha22
Lieutenant JG PriscilaCunha22 Lieutenant JG
15
Back to Solutions for Motor Management
Posted: ‎2022-09-14 02:44 AM . Last Modified: ‎2023-06-09 04:24 AM
1
1322
  • Low Voltage AC Drives
LeoLazzaro
Lieutenant
Posted: ‎2024-11-06 04:59 AM
Hi Sim89 :  Using Cia402 or IO profile . you have to select Cxx bit (virtual input) instead of digital input at the moment that you configure the function . Lets take an example DC injection function via Mobdbus communication  In this case we want to use Bit13 to activate the DC injection via modbus => we have to go to the dCi parameter and set C113.  . Please see below the screen shot from modbus manual and programing manual
Important: Number of the Cxxx  bit is different if you use IO profile or for different com protocols.  the example is only for modbus and CIA402 . For other protocol  please check the number in the attached pictures below  or in the correct communication manuals depding the selected protocol .
Source Document :
https://download.schneider-electric.com/doc/EAV64325/ATV600_Modbus_manual_EN_EAV64325_01.pdf
https://download.schneider-electric.com/doc/EAV64318/ATV600_Programming_Manual_EN_EAV64318_11.pdf
LeoLazzaro
Lieutenant
Source Document :