Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Help with SAFF on ATV320

Solutions for Motor Management

Get support to configure, troubleshoot, update or upgrade your motor management solution built with Altivar variable speed drives and Tesys devices to start, control, protect and monitor Low Voltage and Medium Voltage motors and loads, covering direct start, soft start and variable speed control.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Solutions for Motor Management
  • Help with SAFF on ATV320
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BJacqz
Commander BJacqz Commander
49
LeoLazzaro
Lieutenant LeoLazzaro Lieutenant
16
PriscilaCunha22
Lieutenant JG PriscilaCunha22 Lieutenant JG
15
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Solutions for Motor Management
Start a Topic
Solved
fritz_kaker
fritz_kaker
Cadet

Posted: ‎2024-07-19 02:39 PM

0 Likes
2
3378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-19 02:39 PM

Help with SAFF on ATV320

Customer has an Altivar320 drive that randomly gives SAFF error.

 

power cycling will sometimes clear the fault, only to have it come back immediately, or randomly in a few minutes or a few hours.

 

The customer will only let their engineers connect a laptop to their equipment, so I am unable to use SOmove to look at the registers, and their engineer is in another state.

 

The graphic display terminal is not available either, so all I have is the hmi.

 

the factory jumper is connected from P24 to STO, and 24v is present there.

In an attempt to eliminate the motor as a cause, removed the motor wires from the drive, and I still get SAFF on power up.

 

Any tips to resolve this before replacing the drive?

Labels
  • Labels:
  • Drives & Motor Control
  • Low Voltage AC Drives
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Ahmed_Alzafer
Lieutenant JG Ahmed_Alzafer Lieutenant JG
Lieutenant JG

Posted: ‎2024-10-31 06:56 AM

0 Likes
0
3199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-31 06:56 AM

Hello 

 SAFF status on the drive means after the drive was powered up in RDY  or is running, and someone opened one of the safety STO, SLS, SS1 safety inputs.
To clear the SAFF, power down the drive and make sure any assigned safety inputs are turned on or jumper to +24vdc before you power the drive back up. (For Testing purpose only).
 
Other things to check that can trigger a SAFF
Make sure Debounce time and response time are set to 0 for both to deactivate this function. Again, if the values are out of range, it can trigger a SAFF status.
unfortunately, Safety programming can only be done using SoMove programming software.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BJacqz
Commander BJacqz Commander
Commander

Posted: ‎2024-08-22 02:50 AM

0 Likes
0
3324
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-22 02:50 AM

I am not specialist on this topic but may be this document can help you on this matter. I advise then to contact your local Schneider representative.

ATV32 How to Diagnose a SAFF fault.pdf

Bruno Jacqz, Drives training leader
Reply

Link copied. Please paste this link to share this article on your social media post.

Ahmed_Alzafer
Lieutenant JG Ahmed_Alzafer Lieutenant JG
Lieutenant JG

Posted: ‎2024-10-31 06:56 AM

0 Likes
0
3200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-31 06:56 AM

Hello 

 SAFF status on the drive means after the drive was powered up in RDY  or is running, and someone opened one of the safety STO, SLS, SS1 safety inputs.
To clear the SAFF, power down the drive and make sure any assigned safety inputs are turned on or jumper to +24vdc before you power the drive back up. (For Testing purpose only).
 
Other things to check that can trigger a SAFF
Make sure Debounce time and response time are set to 0 for both to deactivate this function. Again, if the values are out of range, it can trigger a SAFF status.
unfortunately, Safety programming can only be done using SoMove programming software.
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore