Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Get support to configure, troubleshoot, update or upgrade your motor management solution built with Altivar variable speed drives and Tesys devices to start, control, protect and monitor Low Voltage and Medium Voltage motors and loads, covering direct start, soft start and variable speed control.
Search in
Posted: 2020-06-06 10:17 PM . Last Modified: 2021-03-16 09:48 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-06-06 10:17 PM . Last Modified: 2021-03-16 09:48 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-06-08 11:10 PM
Have to say that a motor may be out of my knowledge, but many times you could check in the datasheet, the nominell voltage for the supply if given, but also a procent over and under voltage that they specify.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-15 10:31 AM
Hello, yes you can. If the motor is specified at 415V but you use it at 400 this is 3.6% lower value. For the same load power the motor will take higher current, to compensate for the lower voltage, but it is reasonable, and the motor can operate continuously. Motors can tolerate ~10% voltage variation, if nothing else is specified. Also, let's not forget that often motors are over-specified for the application and in fact do not run at full power, meaning its current will actually be lower than rated.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-06-08 11:10 PM
Have to say that a motor may be out of my knowledge, but many times you could check in the datasheet, the nominell voltage for the supply if given, but also a procent over and under voltage that they specify.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-15 10:31 AM
Hello, yes you can. If the motor is specified at 415V but you use it at 400 this is 3.6% lower value. For the same load power the motor will take higher current, to compensate for the lower voltage, but it is reasonable, and the motor can operate continuously. Motors can tolerate ~10% voltage variation, if nothing else is specified. Also, let's not forget that often motors are over-specified for the application and in fact do not run at full power, meaning its current will actually be lower than rated.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.