Dears
I have ATV32H075n4 drive and i wont to tack backup for the parameters and download this backup to the new drive
how can i do that
Best Regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-18 04:45 AM
There are several ways to do this action on our Altivar products.
One can be to use a dedicated tool (name is downloader), this is a dedicated tool, hardware to be conected to drive, take the drive configuration and then conected to another to reproduce the same configuration in the next drive.
Another possibility is to download the freeware SoMove software available on internet. in addition, you have to download ATV32 DTM.
Afterward, you can use Ethernet cable between your computer and Altivar to take the configuration, name it, and reproduce it on another Altivar.
Nota : there is one DTM per type of device (ATV12, ATV32, ATV320, ATV600...).
Feel free to have a look on existing "how to video" about the SoMove subject, it will help you to better understand this upload/dowload topic : https://www.youtube.com/watch?v=u6-CbjcifcU
Feel free also to visit our knowledge center. There are some examples of conecting SoMove with ATS22 (principle is equivalent) : https://community.se.com/t5/Industrial-Automation-How-to/How-to-connect-and-configure-ATS22-with-SoM...