Atv71

Solutions for Motor Management

Get support to configure, troubleshoot, update or upgrade your motor management solution built with Altivar variable speed drives and Tesys devices to start, control, protect and monitor Low Voltage and Medium Voltage motors and loads, covering direct start, soft start and variable speed control.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Solutions for Motor Management
  • Atv71
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BJacqz
Commander BJacqz Commander
49
LeoLazzaro
Lieutenant LeoLazzaro Lieutenant
16
PriscilaCunha22
Lieutenant JG PriscilaCunha22 Lieutenant JG
15
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Solutions for Motor Management
Start a Topic
Solved
YOUNUS
Crewman YOUNUS
Crewman

Posted: ‎2023-03-26 03:01 AM . Last Modified: ‎2023-03-30 04:54 AM

0 Likes
7
3243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-26 03:01 AM . Last Modified: ‎2023-03-30 04:54 AM

Atv71

Dear sir 

We are using atv71 drive for crane application long travel purpose 4 motors connected together each motor 5.5 kw

And vfd 30KW 

2 Motors near the panel and motors 30 meters faraway 

When we start the crane only current increase frequency remains zero.

If we disconnect 2 motors crane working fine. 

If 4 motors connect crane stops working???

Please me 

Labels
  • Labels:
  • Low Voltage AC Drives
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
LeoLazzaro
Lieutenant LeoLazzaro Lieutenant
Lieutenant

Posted: ‎2023-03-30 09:04 AM

1 Like
1
3215
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-30 09:04 AM

Hi I think is necesary to reach the  local customer care center in your region  for this case, we will need more information, model of the drives , configuration , etc. 

I can recommend you :

                                    1) try to keep same cable distance

                                    2) check the sense of rotation of each motor , if you can check one by one  will be better . Maybe 2  of them are rotating  in opposite direction then when 4 are working current increase but no movement.

                                    3) check Motor control Menu parametrization as you have 4 motor in parallel you have to take care in the data that you enter in the drive , drive does not know that you have 4 motor , he see all motors as 1  bigger.  Test SVC and U/F to check if there is some difference . 

                                     4) I guess all motors are pulling of same load if you use SVC please put Slip compensation in 0% to share the load between all motors. 

 

Thank you 

B.R.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BJacqz
Commander BJacqz Commander
Commander

Posted: ‎2023-03-30 09:00 AM

0 Likes
1
3215
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-30 09:00 AM

First idea I have from your description would be to check if motors are all running in same direction when you activate. To check it, disconnect 2 of them (see the direction), then test with two other one.

Another topic would be to check what is the current entered in the drive (should be the total of motors in paralell). What about the thermal protection, how is it done ?

Bruno Jacqz, Drives training leader
Reply

Link copied. Please paste this link to share this article on your social media post.

LeoLazzaro
Lieutenant LeoLazzaro Lieutenant
Lieutenant

Posted: ‎2023-03-30 09:04 AM

1 Like
1
3216
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-30 09:04 AM

Hi I think is necesary to reach the  local customer care center in your region  for this case, we will need more information, model of the drives , configuration , etc. 

I can recommend you :

                                    1) try to keep same cable distance

                                    2) check the sense of rotation of each motor , if you can check one by one  will be better . Maybe 2  of them are rotating  in opposite direction then when 4 are working current increase but no movement.

                                    3) check Motor control Menu parametrization as you have 4 motor in parallel you have to take care in the data that you enter in the drive , drive does not know that you have 4 motor , he see all motors as 1  bigger.  Test SVC and U/F to check if there is some difference . 

                                     4) I guess all motors are pulling of same load if you use SVC please put Slip compensation in 0% to share the load between all motors. 

 

Thank you 

B.R.

Reply

Link copied. Please paste this link to share this article on your social media post.

Laureano
Crewman Laureano Crewman
Crewman

Posted: ‎2023-03-31 04:04 AM

0 Likes
0
3201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-31 04:04 AM

I recommend having a look at the attached document.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

YOUNUS
Crewman YOUNUS
Crewman

Posted: ‎2023-05-08 09:41 PM

In response to BJacqz
0 Likes
0
3086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-08 09:41 PM

 

Thanks 

Reply

Link copied. Please paste this link to share this article on your social media post.

YOUNUS
Crewman YOUNUS
Crewman

Posted: ‎2023-05-08 09:41 PM

In response to LeoLazzaro
0 Likes
0
3086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-08 09:41 PM

Thanks 

Reply

Link copied. Please paste this link to share this article on your social media post.

YOUNUS
Crewman YOUNUS
Crewman

Posted: ‎2023-05-08 10:00 PM

0 Likes
0
3079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-08 10:00 PM

Dear sir 

We are using ATV 71 37kw drive for crane hoist application 

We are facing problem while crane down function operation sound coming from motor.

Up operation no sound. 

With loads little bit more sound. no load condition little bit less sound coming 

We check all mechanical bearings gear box every thing 

I feel motor sound 

Motor have encoder 

Parameter (Ctt) motor control type is FuC

Please give me some advice 

Reply

Link copied. Please paste this link to share this article on your social media post.

PCDTC
Crewman PCDTC
Crewman

Posted: ‎2024-04-27 05:13 AM

0 Likes
0
2147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-27 05:13 AM

for heavy loads that need torque you should lower the ramp up time and dont start from zero hz make min frequency 5 hz at least 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore