If the Altivar 630 faults after a power failure but there was no run command present at time of power failure, will the drive reset once a run command is present such as a call for a lag pump or a pump sequence change?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-03-13 08:10 AM
Hi LouD :
Thanks for your question .
The complete drive will switch off after main power supply loss , then drive will store in the fault history memory USF ( Undervoltage fault) . but USF is cleared as soon power supply is recovered and it will be operable for next run order.
For other hand , ATV630 has Automatic Restart function(ATR) for other type of faults,. Please refer to the ATV600 programming manual to know more about this funtion
Thank you in advance
Leonardo Lazzaro
Global Offer Manager ATV Process
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-03-13 08:10 AM
Hi LouD :
Thanks for your question .
The complete drive will switch off after main power supply loss , then drive will store in the fault history memory USF ( Undervoltage fault) . but USF is cleared as soon power supply is recovered and it will be operable for next run order.
For other hand , ATV630 has Automatic Restart function(ATR) for other type of faults,. Please refer to the ATV600 programming manual to know more about this funtion
Thank you in advance
Leonardo Lazzaro
Global Offer Manager ATV Process