Posted: 2024-11-19 12:08 AM
Hello everybody,
My ATS48C17Q (170A) is experiencing a PHF error when I press RUN. I have restored the default settings and loaded the old program, but the issue persists. Currently, I've installed a new soft starter and it runs OK. The old soft starter runs fine when I adjust the SST (Small motor) parameter to test a small motor.
Experts, please help me. Thank you, everyone.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-12-18 05:57 AM
Hello
If the fault is detected after completion of the acceleration ramp, ensure the proper connection of the shorting contactor, if used. The output of the the shorting contactor must be connected to terminals A2-B2-C2, and must close within 200 milliseconds of reaching full speed.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-12-20 04:58 AM
Do you have a contactor upstream or downstream of the ATS?
FA176691
The PHF fault represents the detection of a phase loss downstream or upstream of the starter.
It is necessary to check the upstream/downstream and motor wiring and the intervention of any protection devices.
If the starter Start command is passed together with the line contactor closing command, it is possible that the ATS48 starter goes into PHF fault: in this case it is sufficient to delay the closing of the Start command.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-18 03:19 AM
PHF = Phase Fault (phase loss or imbalance) on ATS48.
Since your new soft starter works fine on the same motor, the old unit likely has an internal issue (failed SCR or current‑measurement board). SSt works because it lowers detection thresholds, masking the fault.
Quick fix path:
Check if PHF appears instantly → likely SCR or measurement board fault.
Verify phase currents in SUP menu; one phase probably reads zero.
If confirmed, the old ATS48 needs repair or replacement (power board or measurement board).
Link copied. Please paste this link to share this article on your social media post.