Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Get support to configure, troubleshoot, update or upgrade your motor management solution built with Altivar variable speed drives and Tesys devices to start, control, protect and monitor Low Voltage and Medium Voltage motors and loads, covering direct start, soft start and variable speed control.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-03 03:05 AM
Hellow everybody.
I have a problem whith LTMR27EFM, when we change to remote control (I.6 input ON) with Ethernet IP from PLC CompacLogix is working (run, O.1, O.2 e.t.c) but when I physicaly imitate communication loss with disconecting the wire UTP, the outputs motor start LO.1 and LO.2 are not Shout down or not swhitching but LO.1 and LO.2 are state "ON" (comand from CompacLogix).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-22 10:29 AM
Hi Nurali,
Wish you are very well.
It seems to me that what is missing is the primary IP address as indicated on the user manual page 26 and 29 from the link as follow:
Hope this help. If the problem persists, I suggest that you open a technical case with Schneider at your country and include the complete SoMove file exported for a deeper investigation.
Best Regards,
Neide
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-22 10:29 AM
Hi Nurali,
Wish you are very well.
It seems to me that what is missing is the primary IP address as indicated on the user manual page 26 and 29 from the link as follow:
Hope this help. If the problem persists, I suggest that you open a technical case with Schneider at your country and include the complete SoMove file exported for a deeper investigation.
Best Regards,
Neide
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-12 02:09 AM
Hi Neide,
I hope you're doing well.
I’d like to raise a concern regarding the Tesys LTMR behavior following a communication loss with the PLC. After a COM LOSS event, the remote start command (bit 704.0) retains its last value, even though the motor stops as per the configured fail-safe response. However, once communication with the primary PLC IP is restored, the LTMR immediately executes the retained start command, causing the motor to restart unexpectedly. It then resumes following PLC commands thereafter.
This behavior poses a significant safety risk in the field, as the unintended motor restart could lead to hazardous conditions.
Is there a recommended method or function to automatically clear or reset bit 704.0 upon communication loss, to prevent this scenario? Any guidance or best practices to ensure safe recovery behavior would be greatly appreciated.
Best regards,
Palanikumar