TeSys T LTMR Ethernet communication loss don't work.
Hellow everybody.
I have a problem whith LTMR27EFM, when we change to remote control (I.6 input ON) with Ethernet IP from PLC CompacLogix is working (run, O.1, O.2 e.t.c) but when I physicaly imitate communication loss with disconecting the wire UTP, the outputs motor start LO.1 and LO.2 are not Shout down or not swhitching but LO.1 and LO.2 are state "ON" (comand from CompacLogix).
- Parametr network port fallback action setting = LO1, LO2 off
- Network protocol = Ethernet IP
- Network port trip enable = enable
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-22 10:29 AM
Hi Nurali,
Wish you are very well.
It seems to me that what is missing is the primary IP address as indicated on the user manual page 26 and 29 from the link as follow:
Hope this help. If the problem persists, I suggest that you open a technical case with Schneider at your country and include the complete SoMove file exported for a deeper investigation.
Best Regards,
Neide
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-22 10:29 AM
Hi Nurali,
Wish you are very well.
It seems to me that what is missing is the primary IP address as indicated on the user manual page 26 and 29 from the link as follow:
Hope this help. If the problem persists, I suggest that you open a technical case with Schneider at your country and include the complete SoMove file exported for a deeper investigation.
Best Regards,
Neide