Hello
Independently from what I put into "Username:" field during installation in logs I always see "sa" user.
Link copied. Please paste this link to share this article on your social media post.
install as local admin.
in sql management studio, set local admin to have db create permissions.
during install, set sc to use windows implicit.
test your connection using odbc instead of sc install wizard to ensure connection works (or, test password in sql management studio logon.
ensure sc database gets created in sql after sc install.