Unexpected character encountered while parsing value

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • Unexpected character encountered while parsing value
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
sesa180908_brid
Commander sesa180908_brid Commander
34
ardak
ardak Schneider Alumni (Retired)
34
View All

Recommended Forums

  • Intelligent Devices Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SmartConnector Forum
Start a Topic
Solved
SteveGregory
Commander SteveGregory Commander
Commander

Posted: ‎2018-09-25 07:03 PM

0 Likes
2
1854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-09-25 07:03 PM

Unexpected character encountered while parsing value

I am getting the following error when requesting log data via the SboRestProvider

 

"Unexpected character encountered while parsing value"

 

It is happening on about 10% of logs.

 

Has anyone seen this before?

Attachments
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2018-10-18 12:12 PM . Last Modified: ‎2018-10-18 12:21 PM

0 Likes
0
1839
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-10-18 12:12 PM

Hi Steven,

 

I looked into this, and I believe it has to do with the amount of trend data that is being read by the server and then cached in the In-Memory cache in Smart Connector.

 

What happens is that every time Trends Samples are requested, Smart Connector will send requests for that range of values and save them in the In-Memory cache. These values that are saved in the In-Memory cache are saved permanently. As you can imagine over time, these caches can get quite gigantic per trend log. I am thinking that eventually, it gets so huge that the Json Serializer cannot deserialize the whole object, and we end up with this error, also may explain issue with certain time ranges never coming back, perhaps saving the data into the cache doesn’t happen after a certain size, and it is pulling out stale data. (but somehow deserializes OK)

 

In any case, the Rest Providers (both EWS and SOAP), likely will have the same issue as they both cache trend samples from EBO.

 

I am working on a ‘fix’ that will only save retrieved trend samples for only 5 minutes before removing them. That way, it should be there long enough to finish any ‘paging’ a client wants, but at the same time, removing them as to not let the in-memory cache get gigantic, and become un-manageable.

 

This release should be available today or tomorrow.


Regards,

 

-Jeff

See Answer In Context

Reply
Replies 2
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2018-09-25 10:09 PM

0 Likes
0
1850
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-09-25 10:09 PM

Hi Steven,

 

Any way you can turn on Trace level logging in Smart Connector as well as turning on CspClient logging (assuming SboRestProvider) or EwsClient logging (assuming SoapRestProvider). I am wondering what SBO is actually returning.

 

Regards,

 

-Jeff

Reply
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2018-10-18 12:12 PM . Last Modified: ‎2018-10-18 12:21 PM

0 Likes
0
1840
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-10-18 12:12 PM

Hi Steven,

 

I looked into this, and I believe it has to do with the amount of trend data that is being read by the server and then cached in the In-Memory cache in Smart Connector.

 

What happens is that every time Trends Samples are requested, Smart Connector will send requests for that range of values and save them in the In-Memory cache. These values that are saved in the In-Memory cache are saved permanently. As you can imagine over time, these caches can get quite gigantic per trend log. I am thinking that eventually, it gets so huge that the Json Serializer cannot deserialize the whole object, and we end up with this error, also may explain issue with certain time ranges never coming back, perhaps saving the data into the cache doesn’t happen after a certain size, and it is pulling out stale data. (but somehow deserializes OK)

 

In any case, the Rest Providers (both EWS and SOAP), likely will have the same issue as they both cache trend samples from EBO.

 

I am working on a ‘fix’ that will only save retrieved trend samples for only 5 minutes before removing them. That way, it should be there long enough to finish any ‘paging’ a client wants, but at the same time, removing them as to not let the in-memory cache get gigantic, and become un-manageable.

 

This release should be available today or tomorrow.


Regards,

 

-Jeff

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore