Sometimes, SmartConnector doesn't start at Windows Startup

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • Sometimes, SmartConnector doesn't start at Windows Startup
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
ardak
ardak Schneider Alumni (Retired)
34
sesa180908_brid
Commander sesa180908_brid Commander
34
mike_meirovitz
Commander mike_meirovitz
21
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Building Operation

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SmartConnector Forum
Solved
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2021-03-11 01:01 AM

0 Likes
5
1276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-11 01:01 AM

Sometimes, SmartConnector doesn't start at Windows Startup

Sometimes (for example, once in 9 Windows restarts), the SmartConnector doesn't start at Windows startup.

If you look at the service status is looks like it is running, but our processor that is defined as "Runs On Start = True" doesn't start.

Only if I stop/start the SmartConnector service our processor will start.

 

The SmartConnector service is defined with 2 dependent services:

SQL-Server

Building Operation 3.1 Enterprise Server.

 

Any idea what to do?

 

Thank you.

 

Mike

 

  • Thumbnail of EcoStruxure™ Building Operation
    Schneider Electric
    EcoStruxure™ Building Operation
View products (1)
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2021-03-18 03:12 PM

0 Likes
0
1257
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-18 03:12 PM

Hi Jeff,

 

Thank you. 

 

Regards,

 

Mike

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 5
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2021-03-11 04:48 AM

0 Likes
4
1272
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-11 04:48 AM

Hi Michael,

 

I am not sure what would cause this! Some questions.

 

- What version of Smart Connector is this occurring on?

- Is this new behavior?

- Is there anything in the log that may show what is happening here?

- What type of processor is this? Is it long running?

- Is this processor also running on a schedule?

 

Best Regards,

 

-Jeff

 

 

 

Tags (1)
  • Tags:
  • english
Reply
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2021-03-11 08:04 AM

0 Likes
3
1269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-11 08:04 AM

Hi Jeff,

 

Thank you for your answer. See my answers below.

 

1. The version of the SmartConnector is 2.4.25.

2. I saw it also in the past.

3. See the attached log file. I didn't see anything special.

4. This is the setup processor that is part of our EBO-OPC Client EWS Server. The setup processor is defined as "Runs on Start = True" and "Run on Schedule = False". The Setup processor starts the Update processor after it completes creating the EWS folders and items. The Update processor is defined as "Runs on Start = True" and "Run on Schedule = False".

5. Yes. The Update processor is long running.

6. No, both processors are not running on Schedule.

7. If I start the Setup processor manually, it will start and work properly.

 

Thanks.

 

Mike

 

Attachments
2021-03-11 - Copy.log
Tags (1)
  • Tags:
  • english
Reply
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2021-03-18 04:03 AM

0 Likes
2
1263
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-18 04:03 AM

Hi Jeff,

 

Still struggling with this issue. I noticed this error in the SmartConnector log file after I have restarted windows (at 10:55:56).

Any idea what is causing this error? The SmartConnector log file is attached.

 

2021-03-18 10:56:00.8025,Debug,EwsConsume,<no principal>,GetAlarmEvents,6614d29b-845d-4798-b546-1e80c509ca04,Response,{"GetAlarmEventsResponseStatus":{"MoreDataAvailable":false,"MoreDataRef":"","LastUpdate":"8d62ea0e-7f47-457a-8db4-cc93586e23ce|1097","NeedsRefresh":false},"GetAlarmEventsAlarmEvents":{"AlarmEvent":[{"ID":"/Server 1|/Server 1/MyValues/Building/18thTemp Out of Range Alarm|c600f85b-0b60-4d4e-931b-548f7771f032","SourceID":"02/Server 1/MyValues/Building/18thTemp Out of Range Alarm","SourceName":"18thTemp Out of Range Alarm","Acknowledgeable":"0","TimeStampOccurrence":"2021-01-11T16:21:37Z","TimeStampTransition":"2021-01-11T16:23:39Z","Priority":"100","State":"2","Type":"","Message":"18th floor. Temperature too high"},{"ID":"/Server 1|/Server 1/MyValues/Building/BuildingTempratureReport Change of State Alarm|34c5c783-c53b-48ec-859c-c17297a2c375","SourceID":"02/Server 1/MyValues/Building/BuildingTempratureReport Change of State Alarm","SourceName":"BuildingTempratureReport Change of State Alarm","Acknowledgeable":"0","TimeStampOccurrence":"2021-01-11T16:25:11Z","TimeStampTransition":"2021-01-11T16:25:58Z","Priority":"100","State":"2","Type":"","Message":"Temp. Report"},{"ID":"/Server 1|/Server 1/EBO OPC Client*8601|3bcf49cf-2327-46e0-8fdc-ee7219ba1309","SourceID":"02/Server 1/EBO OPC Client*8601","SourceName":"EBO OPC Client","Acknowledgeable":"1","TimeStampOccurrence":"2021-03-12T18:59:10Z","TimeStampTransition":"2021-03-12T19:05:01Z","Priority":"100","State":"1","Type":"System alarm","Message":"System alarm: SOAP-ENV:Sender.EWSv1232:SCWS.EWSv1232:INVALID_SUBSCRIPTION Gsoap_Communication__Error: 12 Invalid SubscriptionId parameter: CWS Value Poll failed [8601]"},{"ID":"/Server 1|/Server 1/9 Tags/Analog Value Out of Range Alarm|7c26c588-d40b-4d25-8f44-830773cacd27","SourceID":"02/Server 1/9 Tags/Analog Value Out of Range Alarm","SourceName":"Analog Value Out of Range Alarm","Acknowledgeable":"0","TimeStampOccurrence":"2021-01-19T14:44:49Z","TimeStampTransition":"2021-03-13T16:47:32Z","Priority":"100","State":"2","Type":"","Message":"Too low"},{"ID":"/Server 1|/Server 1/MyValues/Building/11thTemp Out of Range Alarm|a90ee17a-db51-4082-9ed5-29b96d7591c0","SourceID":"02/Server 1/MyValues/Building/11thTemp Out of Range Alarm","SourceName":"11thTemp Out of Range Alarm","Acknowledgeable":"1","TimeStampOccurrence":"2021-03-14T18:46:25Z","TimeStampTransition":"2021-03-14T18:48:19Z","Priority":"100","State":"3","Type":"","Message":""},{"ID":"/Server 1|/Server 1/MyValues/Building/10thTemp Out of Range Alarm|7c37cc1d-9d56-41a4-9a70-8c829d1fca2c","SourceID":"02/Server 1/MyValues/Building/10thTemp Out of Range Alarm","SourceName":"10thTemp Out of Range Alarm","Acknowledgeable":"1","TimeStampOccurrence":"2021-03-13T18:23:25Z","TimeStampTransition":"2021-03-16T06:31:35Z","Priority":"100","State":"1","Type":"","Message":"10th floor. Temperature too high"},{"ID":"/Server 1|/Server 1*7|2adb61fd-49ad-4e91-a0c5-6b78653d891d","SourceID":"02/Server 1*7","SourceName":"Server 1","Acknowledgeable":"1","TimeStampOccurrence":"2021-03-13T17:10:51Z","TimeStampTransition":"2021-03-16T18:19:24Z","Priority":"100","State":"1","Type":"System alarm","Message":"System Alarm: System warm start [7]"}],"Metadata":null},"version":"1.2"},

 

Thank you!

 

Mike

Attachments
2021-03-18.log
Tags (1)
  • Tags:
  • english
Reply
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2021-03-18 10:00 AM

0 Likes
1
1260
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-18 10:00 AM

Hi Michael,

 

From the log, this is not a Smart Connector error, but an alarm that your Smart Connector processor is receiving from EBO.

 

What this means is likely that when EBO sent out an EWS GetNotifications request, it got an INVALID_SUBSCRIPTION error. This should cause the EBO EWS client to resubscribe to the same points.

 

Best Regards,

 

-Jeff

Tags (1)
  • Tags:
  • english
Reply
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2021-03-18 03:12 PM

0 Likes
0
1258
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-18 03:12 PM

Hi Jeff,

 

Thank you. 

 

Regards,

 

Mike

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login